1 - 8 of 8 Posts
I need to add a low mount air combustion vent and a high mount air exchange vent, both to the outside, in my enclosed oil fired boiler utility closet.
The spec stickers on the Peerless boiler state the max at 129k btu's.
If I need 1"sq/2000btu's for horizontal duct that would be a 65sq in.
8"x8" or 10" round.
If possible, I would instead like to add a 4" round with an in-line duct fan to save what little space I have.
How would I convert the additional cfu's from the fan into the amount of square inches I need and know what size cfu fan to get?
· In Loving Memory
Adding a 4" round with an inline fan would not meet code. Since if the fan failed, the boiler would still run. Unless you have an interlock that prevents the boiler from running unless the fan is running.
What are you calling "a high mount air exchange vent"?
· GC/Master Plumber/Mech
I think he is saying one horz duct high and one low.
If I were to do this I would have motorized dampers with proving circuits so you can shut off the cold air when not in use.
· In Loving Memory
That would be the better way to do it.
· In Loving Memory
Yes, it has an interlocking switch. That must prove the fan is bring in air before it wil allow the burner to operate. Its UL approved.
1 - 8 of 8 Posts