Discussion Starter · #1 ·
I just installed a Honeywell RTH2300 in my home to replace an old mercury unit. It appears to be somewhat working, but the AC/Heat will not shut off. For example, it is set at 75 and the ac keeps running down indefinitely. Also, when the thermostat is switched to the 'off' position, the heating/ac unit keeps running and stays on.

I have read the owners manual and installation guide cover to cover and nothing seems to jump out as something I did wrong. Any help would be appreciated!
 

·
Registered
Joined
·
8 Posts
Discussion Starter · #5 ·
Ok, can do. I was going to, but I wanted to ensure it worked properly first. I didn't want to cut it, later need it, and wish I had not have done so. Is this the problem?
 

·
Registered
Joined
·
8 Posts
Discussion Starter · #7 ·
Alright, the red and green were not touching, but they were close, so I removed the excess copper, cleaned up in there a bit, and hooked everything back in. The unit appears to be functioning normally now. Thanks so much for your help!
 