some of you may remember me previous post about my "rats nest" breaker panel. I'm starting to get ready for running the new wires and mounting the new subpanel inside the house and I need some help with how this will all tap in to the existing breaker panel. Here's how it looked when I first started...


...and here's how it looks now that I've done a bit of cleanup with a vacuum


There's a TON of nesting still up inside and behind the meter and I'm probably going to have the power company come and clean that out for me as I don't think I'm allowed behind there...

So here's my plan: I'm going to run a new heavy line from this panel to a new subpanel inside my house and slowly begin running new circuits out to each room as we remodel them. This way, I'm running new electrical while keeping the old in place -abandoning circuits one at a time. Eventually, there will be no live circuits on the original panel -just the meter.

Here's a shot from the inside of the house (back of the panel):


So here's some of my concerns: I'm not sure where I'd tap into the existing power feed. Would I need to access the wiring behind the meter as opposed to the two large black leads in the center of the existing breaker panel? If I need to go behind the meter, maybe I'll have the power shut off at the pole by Edison and then have them go in and clean out the back of the meter (all the old rat's nest bedding) and run new power leads at the same time before they switch it back on?

Any ideas would be great!
 

· Registered
Joined
·
168 Posts
Discussion Starter · #5 ·
Oh yeah, a totally valid question. I have a gas range/oven, gas water heater, and gas dryer. The house is currently 1600sf and I'm going to be bringing right up to 2000 by the time I'm done. Can I bypass that breaker? I'd eventually like to abandon the entire panel and just leave the meter. Will I still need a breaker on the outside of the house?
 

· Registered
Joined
·
2,294 Posts
That looks like a split bus panel.

The 2 pole 30 probably feeds the right side of the panel.

The left side of the bus has no disconnect. It's fed directly from the meter (above),

The biggest circuit you are going to be able to run will ba 100 amps due to breaker size limitation.

I would just run a 60 amp sub panel circuit to the new panel.

I would feed all your new heavy 240V circuits (AC, Rrange, dryer, WH etc) from the main panel.

Id use a full size breaker for the sub and AC, You will have to use thin breakers for the two remaining 240V circuits.

Run a 6/3 (60A) cable to the new sub. Put the breaker on the "main" side of the service. Isolate the neutrals in the sub and you are done. Upgrage your grounding/bonding while you're at it.
 

· Registered
Joined
·
168 Posts
Discussion Starter · #8 ·
I mean, after I manage to replace all of the currently live circuits that are running through this breaker box, will I be able to remove the guts and just leave the meter in this box? I'd sure like to. I don't think that Edison needs the ability to access the master breaker from the outside of my house anyways so maybe I'm just asking stupid questions right now. What I was asking was if there still needs to be a master breaker at this panel (that is now facing the outside of my house). I'm trying to move the breakers to the inside of the house so I won't have any more "rat's nest" problems in the future (as well as modernize the materials and maybe even bring it up to code!). The box is steel. The top half contains the meter (and a bunch of rats nesting material from what I can peek in to see from below. The lower half contains the breaker rail you see pictured above.
 

· Registered
Joined
·
2,294 Posts
OK


Left to right, it looks like...

2 pole mystery breaker

2 pole AC breaker

3 single pole breakers

2 pole (30?) feeding the remainder of the panel (split bus?)

5 single poles

1 two pole 30 (thin)

1 twin 20 (2 120v 20A circuits)

1 single pole.

after I manage to replace all of the currently live circuits that are running through this breaker box, will I be able to remove the guts and just leave the meter in this box?
You need a main outside.

A) Local code will likely require it.
B) You need to attach your sub panel feeder to something so it will have to be a breaker.
 

· Registered
Joined
·
168 Posts
Discussion Starter · #10 ·
That looks like a split bus panel.

The 2 pole 30 probably feeds the right side of the panel.

The left side of the bus has no disconnect. It's fed directly from the meter (above),

The biggest circuit you are going to be able to run will ba 100 amps due to breaker size limitation.

I would just run a 60 amp sub panel circuit to the new panel.

I would feed all your new heavy 240V circuits (AC, Rrange, dryer, WH etc) from the main panel.

Id use a full size breaker for the sub and AC, You will have to use thin breakers for the two remaining 240V circuits.

Run a 6/3 (60A) cable to the new sub. Put the breaker on the "main" side of the service. Isolate the neutrals in the sub and you are done. Upgrage your grounding/bonding while you're at it.
How big of a deal would it be to completely bypass this breaker panel? I hate relying on components that are not only decades old but located on the outside of my house.
 

· Registered
Joined
·
2,294 Posts
The reason I would take the high draw loads from the service outside is to minimize the load/wire size for the new sub inside.

The max breaker you are going to find for that panel is 100...maybe 125A.


The existing service is likely 100 or 125 so I guess it wouldn't be any different.
 

· Registered
Joined
·
1,893 Posts
That looks like a split bus panel.

The 2 pole 30 probably feeds the right side of the panel.

The left side of the bus has no disconnect. It's fed directly from the meter (above),

The biggest circuit you are going to be able to run will ba 100 amps due to breaker size limitation.

I would just run a 60 amp sub panel circuit to the new panel.

I would feed all your new heavy 240V circuits (AC, Rrange, dryer, WH etc) from the main panel.

Id use a full size breaker for the sub and AC, You will have to use thin breakers for the two remaining 240V circuits.

Run a 6/3 (60A) cable to the new sub. Put the breaker on the "main" side of the service. Isolate the neutrals in the sub and you are done. Upgrage your grounding/bonding while you're at it.
220/221 help me out here. Is this a 100 or 200 amp service and why do i think I see a 30 amp sp in the panel.
 

· Registered
Joined
·
2,294 Posts
How big of a deal would it be to completely bypass this breaker panel? I hate relying on components that are not only decades old but located on the outside of my house.
You will still probably need a main outside.


Change the service @ about $2k-$3k. DIY for substantially less money, substantially more headache.


If you are all gas, the 125A will do it. If you want to upgrade, now is the time to do it.
 

· Registered
Joined
·
2,294 Posts
220/221 help me out here. Is this a 100 or 200 amp service and why do i think I see a 30 amp sp in the panel.
It a 100 or 125 I believe.

It does look like a 1p30 on the far right.....with a white wire :laughing:


Perp, Turn off the green 2 pole breaker in the middle and test power on all breakers. I am thinking that the right half will shut off and the left half will still be hot.

They did that for the "six switch or less max to kill all power" rule
 

· Registered
Joined
·
168 Posts
Discussion Starter · #16 ·
Yeah, I just got off the phone with my county's electrical inspector. They don't have a code requirement for an outside main breaker (with the Building and Safety Department) but the utility company (Southern California Edison) and the Fire Department do. They want an easy access ability to shut off power to the entire building as well as an external overload protection device just past the meter on the load side. I guess I'm going to have to keep something here in this bay. Still I'd like to eventually replace the entire guts of this box with more modern components. Am I insane for wanting this?
 

· Registered
Joined
·
2,294 Posts
Am I insane for wanting this?
Unrealistic perhaps.:laughing:

I am out of town till Monday. Good luck :thumbup:

but look left of the 100 amp in the middle and the third breaker left of it looks like 12# on a sp 30
The green handles usually mean 30A. That's why I thought it was feeding the other half of the bus. I can't read the numbers on the breakers.

Green used to indicate 30, red= 20 and blue = 15.

If that is indeed a 100 amp main that feeds the whole bus, I would be surprised. If it is, he'd have to place a 100/125 next to it and have two "mains"
 

· Registered
Joined
·
671 Posts
It seems to me, that a better long term solution is to drop in a new meter socket and panel inside the house.

Then from the new panel inside the house, temporarily feed this panel with say, a 60 amp feed.

Ideally, you'd move the A/C and heavy loads over to the new panel so that the temporary feed to this panel can be as small as possible.

Then as you remodel the house and rewire each room, they will be on the new panel.

When you are done, this old panel can be completely removed and you wont have any old components in the middle of your electrical system.

A 200 amp meter socket costs around $40-50. So really, the cost difference isnt going to be that much for DIY.
 

· Registered
Joined
·
168 Posts
Discussion Starter · #19 ·
It seems to me, that a better long term solution is to drop in a new meter socket and panel inside the house.

Then from the new panel inside the house, temporarily feed this panel with say, a 60 amp feed.

Ideally, you'd move the A/C and heavy loads over to the new panel so that the temporary feed to this panel can be as small as possible.

Then as you remodel the house and rewire each room, they will be on the new panel.

When you are done, this old panel can be completely removed and you wont have any old components in the middle of your electrical system.

A 200 amp meter socket costs around $40-50. So really, the cost difference isnt going to be that much for DIY.
Fantastic idea! I think this is exactly what I'm going to do. Thanks everyone for all your help!!
 