I'm replacing our utility sink and wanted to add a standpipe for the washer. Currently the washer drains right into the sink.

As you can see in the pictures, the utility sink connects to the 2" vent stack while the second 2" line is for the kitchen sink and dish washer directly above.

Is it proper to add the stand pipe inline with the utility sink? The stand pipe and full drain (except the lines from the utility sink which would be 1.5") would be 2". Going from left to right, it would be vertical stand pipe, 90 to go horizontal, T for first sink drain, T for second sink drain, trap, then into the vertical drain as it currently stands.

Thoughts?
 

Attachments

· Registered
Joined
·
455 Posts
Discussion Starter · #3 ·
Under IPC code you would need 3 inch pipe for the washer. I do not see any. Hopefully your in a UPC area.
Here's what I found for Ohio.
406.3 Waste connection. The waste from an automatic clothes washer shall discharge through an air break into a standpipe in accordance with Section 802.4 or into a laundry sink. The trap and fixture drain for an automatic clothes washer standpipe shall be a minimum of 2 inches (51 mm) in diameter. The automatic clothes washer fixture drain shall connect to a branch drain or drainage stack a minimum of 3 inches (76 mm) in diameter. Automatic clothes washers that discharge by gravity shall be permitted to drain to a waste receptor or an approved trench drain.

So what happens with these codes if the house was built in 1974? Is it grandfathered in due to its age?
 

· Registered
Joined
·
455 Posts
Discussion Starter · #5 ·
After looking at things a bit more, there is a 3" drain line off to the right about 1' from the sink drain and vent pipe shown in my pictures. The 3" drain line is used for a 1/2 bath, sink, plus a utility sink that is in the garage. The vent is in the wall between the 1/2 bath and garage, so if I tied the standpipe into the 3" drain, could I vent it into the 1.5" vent line that the kitchen and basement utility sink was using?

The other issue is the standpipe would be about 6' away from the 3" drain.
 

Attachments

· Registered
Joined
·
6,647 Posts
After looking at things a bit more, there is a 3" drain line off to the right about 1' from the sink drain and vent pipe shown in my pictures. The 3" drain line is used for a 1/2 bath, sink, plus a utility sink that is in the garage. The vent is in the wall between the 1/2 bath and garage, so if I tied the standpipe into the 3" drain, could I vent it into the 1.5" vent line that the kitchen and basement utility sink was using?

The other issue is the standpipe would be about 6' away from the 3" drain.
A permit and inspection is required if your in an area with an inspection authority.

The stand pipe would need to tie into the three inch. with a 3 by 2 inch tee.
The vent would be between the 3 inch tee and the 2 inch trap for your washer stand pipe. A Tee on its back 2 by 2 by 1.5 the vent

You can tie it into an existing vent as long as that is all it is. A vent does not have anything draining into it from the floor above.

The tie in must be 6 inches above the top of your stand pipe or 6 inches above the flood level rim of the highest fixture in the basement. Normally 42 inches works unless you make a super long stand pipe.

You will need to use a transitional coupling from plastic to cast. Proflex brand or Mission brand are 2 approved types of couplings. You cannot use a all rubber coupling that has radiator clamps.
 

· Registered
Joined
·
455 Posts
Discussion Starter · #8 ·
Thanks for all the explanations! After looking it over some more, it shouldn't be that hard to tie into the 3" drain. Just unbolt the coupling at the floor and cut the 3" vertical drain pipe. Even reinstall shouldn't be too bad as the 3" vertical drain pipe may move up and down a bit since at the top of the wall it starts a horizontal run.

While there are still some additional details to figure out, one that is bugging me is the vent for the standpipe. There is a 1.5" vent stack and a 1.5" vertical drain next to the 3" vertical drain. The attached sketch shows the layout, the standpipe in black is on the far left, there is a 40" wide double utility sink (in blue) followed by the 1.5" vent and drain then the 3" drain. There is enough room between the foundation wall and the utility sink legs to run the stand pipe. I have come up with three options for connecting the standpipe vent.

1) In orange; goes vertical right after the trap, up to the proper height (42" or at least 6" over the highest fill), then shoot across the wall to the drain. Don't like that option as you'll see the vent line.

2) In green; vent somewhere under the utility, run horizontally under the utility sink as high as possible to the other side, turn up, and then into the vent.

3) In purple, vent right after the utility sink, up and into the vent. (preferred option). This would be about 5' from the standpipe.

The question I have is how far from the standpipe and trap does the vent need to be?

Thanks for the help!
 

Attachments

· Registered
Joined
·
6,647 Posts
If your running 2 inch it can be 8 foot from the vent. The vent cannot go horizontal until it is 6 inches above the flood level rim usually 42 inches above the floor. There is no exception to this rule on the vent.
 

· Registered
Joined
·
455 Posts
Discussion Starter · #10 ·
Thanks Ghostmaker. The drain will be 2 inch, but the vent stack it is going into it is only 1.5". Does that change the distance equation?

On top of that, the old utility sink tied into the 1.5 inch vent stack to drain and vent. You can see that in the pic below. The drain on the left is the kitchen drain and just right of it off the Y is the vent/utility sink drain. Will venting the standpipe and having the utility drain on that vent line ok? Something doesn't seem right with that.
 

· Registered
Joined
·
6,647 Posts
show me where you want the utility sink and the washer standpipe.

Basically you will need to run 3 inch as a drain to the point you only have one fixture left. Both fixtures will need to be vented. Depending on how you plan to place all this will make the difference on how it is piped.
 

· Registered
Joined
·
455 Posts
Discussion Starter · #15 ·
show me where you want the utility sink and the washer standpipe.

Basically you will need to run 3 inch as a drain to the point you only have one fixture left. Both fixtures will need to be vented. Depending on how you plan to place all this will make the difference on how it is piped.
From left to right, stand pipe, utility sink, 1.5" drain and vent lines, then 3" drain.
 

Attachments

· Registered
Joined
·
455 Posts
Discussion Starter · #17 ·
Updated the pic with what I'd like to do...

Red is the 2" standpipe and drain (trap not shown) going into the 3" vertical drain line with a tee then the clean out on top of it.

The blue line is a 1.5" vent (with a backwards wye) going up past the standpipe height, and into the 1.5" vertical vent with a tee.

The green is the existing 1.5" utility drain line that attaches to the 1.5" vent line, and will just reuse it.

A bit less complex than trying to tie the utility drain into the standpipe drain and into the 3" stack. Hopefully this will be acceptable.
 

Attachments

· Registered
Joined
·
6,647 Posts
Two tee connections the stand pipe a three inch by 2 tee the Sink a 2 by 1.5 by 1.5 inch tee.

Also two traps, a 2 inch trap on the stand pipe a 1.5 inch trap on the sink..

Just place the three by 2 tee low bush the top to 2 inch then place the second tee the vent is 1.5 inch.

What your doing is called a common vent.
 

· Registered
Joined
·
455 Posts
Discussion Starter · #19 ·
Just finished the supply run. Ended up at Lowe's and I picked up two current no hub connectors. One had a band that was corrugated the other "heavy duty" version was smooth all the way around. This is for connecting the 3" line to the cast iron pipe coming out of the foundation. Is one a better choice than the other?
 