Hi!

I'm a newbie to the electrical trade looking for some advice. Am working on a residential project for a friend dedicating a basement laundry to its own 20A breaker, and want to add a pull-chain light on that circuit.

Does it matter whether the panel line connects to the laundry receptacle first or the light? I wanted to run a junction box for these, but have very limited space (duct obstruction, low ceiling, plumbing placement) - best place to mount the light was before the 20A receptacle in the run. I haven't wired the panel yet, but have the panel line connecting directly to the light fixture as well as the new receptacle.

Any help would be most appreciated!

Thanks,
Andy
 

·
Master Electrician
Joined
·
1,453 Posts
Circuits for laundry receptacles are not allowed to have anything but laundry receptacles on them. No lights, no receptacles for other rooms, etc. Laundry receptacles only.
 

·
Registered
Joined
·
1,893 Posts
Not legal to put lights on the laundry circuit.

210.11(C)(2) Laundry Branch Circuits. In addition to the number
of branch circuits required by other parts of this section, at
least one additional 20-ampere branch circuit shall be provided
to supply the laundry receptacle outlet(s) required by
210.52(F). This circuit shall have no other outlets.
 

·
jschaben
Joined
·
588 Posts
Hi!

I'm a newbie to the electrical trade looking for some advice. Am working on a residential project for a friend dedicating a basement laundry to its own 20A breaker, and want to add a pull-chain light on that circuit.

Does it matter whether the panel line connects to the laundry receptacle first or the light? I wanted to run a junction box for these, but have very limited space (duct obstruction, low ceiling, plumbing placement) - best place to mount the light was before the 20A receptacle in the run. I haven't wired the panel yet, but have the panel line connecting directly to the light fixture as well as the new receptacle.

Any help would be most appreciated!

Thanks,
Andy
Electrically, shouldn't make any difference as they have to be wired in parallel anyway. Code wise, around here, lighting circuits aren't allowed on the same circuits as wall outlets. That's super simplified but essentially the way it is. :)
 

·
Registered
Joined
·
10 Posts
Discussion Starter #5
Not legal to put lights on the laundry circuit.

210.11(C)(2) Laundry Branch Circuits. In addition to the number
of branch circuits required by other parts of this section, at
least one additional 20-ampere branch circuit shall be provided
to supply the laundry receptacle outlet(s) required by
210.52(F). This circuit shall have no other outlets.
Just wanted to say thanks again. I originally read this piece of the Code before I started the project, and should have just left it at that. :wink: I questioned it because I've seen outlets added to this circuit (usually lamps) by people in the trade.
 

·
Registered
Joined
·
1,893 Posts
Just wanted to say thanks again. I originally read this piece of the Code before I started the project, and should have just left it at that. :wink: I questioned it because I've seen outlets added to this circuit (usually lamps) by people in the trade.
The laundry circuit can have more than 1 receptacle in the area and someone can plug in a lamp. You just cannot puts the light fixture and such on the circuit and the circuit cannot leave the area.
 

·
Registered
Joined
·
10 Posts
Discussion Starter #9
The laundry circuit can have more than 1 receptacle in the area and someone can plug in a lamp. You just cannot puts the light fixture and such on the circuit and the circuit cannot leave the area.
Sorry, by lamps, I meant fixtures that are wired directly to the laundry circuit through a junction box, not plugged into the laundry receptacle.

This all started because I referred to another electrician's work on a different job: he wired his basement so that one receptacle running to the kitchen (incidentally, used for a microwave), and three light fixtures are tapping off the laundry breaker in the basement. One of the problems I noticed with that job, is that those lights flicker when the washer is in use.

A problem I've yet to figure out, though, is why lights on another breaker flicker as well when the washer is in use. I thought I had identified every line coming off the washer breaker. Guess not.

Appreciate your input all the same! :thumbsup:
 

·
Master Electrician
Joined
·
1,453 Posts
I’m sorry, I meant the work of the others you gauged it against, not your work.
 

·
JOATMON
Joined
·
15,212 Posts
It's so nice to see everyone kiss and make up....

And on a more serious note.......

While I understand that there is nothing in the code from preventing someone from connecting lights to the same ckt as the outlets (utility, bathroom and fridge excluded), I personally don't ever connect lights on the same ckt as outlets.....nothing worse than tripping the breaker for an outlet and the room going dark. In my house, I took it a step further.....I don't put adjacent rooms on the same lighting ckt. That way, if the breaker trips for the light in one room....you can still get light from the adjacent room
 

·
Registered
Joined
·
1,893 Posts
It's so nice to see everyone kiss and make up....

And on a more serious note.......

While I understand that there is nothing in the code from preventing someone from connecting lights to the same ckt as the outlets (utility, bathroom and fridge excluded), I personally don't ever connect lights on the same ckt as outlets.....nothing worse than tripping the breaker for an outlet and the room going dark. In my house, I took it a step further.....I don't put adjacent rooms on the same lighting ckt. That way, if the breaker trips for the light in one room....you can still get light from the adjacent room
ddawg

It is laundry not utility. Other outlets cannot be on a SABC, nor a dedicated refrigeration or fridge circuit-you mentioned fridge, but not SABC. Bathroom lights can on the same circuit as as the receptacle, if the circuit does not leave the bathroom and the lights are 50% or less of the branch circuit rating.

If these circuits exist, in general- they cannot have other outlets or loads either.
A cord connected range hood.
Central heating.
 

·
A "Handy Husband"
Joined
·
11,829 Posts
scyarch,

The code violations in your last posts are beyond belief. And I am not sure it is wise to post on a public forum that you are doing non-licensed electrical work in a multi-unit rental property.
 