Registered
Joined
·
70 Posts
Discussion Starter · #1 ·
I have a room addition I'd idle to run power to. I'd like to additional 2 20A breakers to my exterior box which would send power to the new room via 2 12/2 romex wires. The box doesn't seem to have any knockouts. Can I cut a hole in the top and attach a plastic conduit to the eve's similar to the Exhisting on the right? The conduit on the right already has maximum wires. The metal conduit on the left is power in from the roof.
Thanks
 

Attachments

·
Registered
Joined
·
1,667 Posts
To further explain a Meyers hub, you need a threaded collar that is attached to the panel with a gasket. You can then use a threaded connector (male adapter) that will be watertight itself. It doesn't look like the existing PVC on the right is compliant unless there is an o ring washer on the adapter.
 

·
Registered
Joined
·
70 Posts
Discussion Starter · #6 ·
Thank you and thanks Jim for that info. Am I permitted to just shave off the yellow protective outter coat on my romex for that short (2 1/2 foot run) through the conduit from the eve to the pannel?
If not, which wire is preferable, solid or stranded wire.
thank you
 

·
Registered
Joined
·
9,504 Posts
I'd run THWN.
Between the very short run and being able to use smaller size conduit, it's probably less expensive than using UF in conduit.

IMO, it would be an easier installation.
 

·
Registered
Joined
·
70 Posts
Discussion Starter · #10 ·
Thanks guys. One last question. What size conduit would I need for six 12GA THWN wires if I go that route? Thanks a million.
 

·
Registered
Joined
·
2,731 Posts
OP has the right idea to go THHN- whoops I mean THWN-2. (same stuff; it's dual labeled). However you only need 1 ground wire - circuits can share it.

You can calculate allowable conduit fill here. 5-6 wires is fine in any conduit made, but 3/4" conduit will pull easier (and install harder lol).

If you want to follow the code to the letter, use UF wire to the 1st junction.
Yes, but UF is quite flat, and flat cable requires excessively large conduit. You must compute conduit fill like it's a round wire of the large dimension (because it twists). And with 2 "wires" in conduit, you are only allowed 30% fill. So for dual 12/2UF, you need (are you sitting down) 1-1/4" conduit. Try it yourself in the conduit fill calc: 12/2 UF is .463" across.
 

·
Registered
Joined
·
70 Posts
Discussion Starter · #13 ·
Thank you for the advice. Especially about only needing one ground wire so I'd only be running 2 whites, 2 blacks and one ground (THWN) in my 3/4" Pvc conduit for the 2 circuts.
 

·
Registered
Joined
·
70 Posts
Discussion Starter · #14 · (Edited)
One more question. Please see the image I found on the net similar to my situation.
In my case, where the Pvc conduit will enter the attic, there is very little room to work with a junction box. Would it be acceptable to run the attic enclosed conduit over several joists (which run perpendicular ) to be able to locate my junction box in a more accessible spot?
 

Attachments

·
Super Moderator
Joined
·
14,528 Posts
You could even extend the conduit further past the elbow.
 
  • Like
Reactions: hotrodjohn71