OK... consider neutral vs ground.
Neutral is the normal current carrying conductor. As you may know, electricity flows in loops. 240V electricity goes out hot1 and comes back on hot2. 120V electricity flows from a hot and comes back on Neutral.
If you want to have both 120V and 240V loads served out of the same box, you must have a Neutral wire. Neutral wires must be white or gray, always.
Equipment Safety Ground is nothing but a safety shield. No current flows on it normally. It is there to be a "fault catcher" so that current is carried back to the panel (and hopefully causes a breaker trip) instead of electrocuting someone or starting a fire. Grounds must be bare or green.
Modern electrical codes require a totally separate neutral vs ground going to a subpanel. They used to allow them to be combined, but a trivial loose connection on neutral would electrify all the grounds, meaning people touching grounded things would get shocked. They considered that "bad".
So, can you state more clearly what you are trying to do? Also several of us would appreciate if you could describe exactly what your loads actually are. We're trying to find a way to pull this off safely.
Also, what are the distances involved?