I would like to add a 40 amp circuit; intent is to charge an EV (Electric Vehicle) in my garage (50 feet from box). In the garage will be a ClipperCreek charger (HCS-40P, 32-amp) plugged into a 240V receptacle (NEMA 14-50). The design limit on the current EV is 13.3 amps, but I’m going heavy in anticipation of a future EV upgrade. I’m planning to use 8-3 cable. My condo was built in 1989 (FYI).

Please provide some input on the selected cable size. Should I go to 6-3?

Before I call the electrician, I would like to secure a general buy-in to my plan on the forum. Anything I’m missing?
Thanks,
TheKingfish
 

· Registered
Joined
·
11,194 Posts
Most home charging stations are 30 rated, so 8 gauge should be fine.
While that may be historically true, more and more vehicles will accept 40 amp chargers, which require 50 amp circuits.

I would run the 6 Awg and use a 40 amp breaker for now. If a new car needs a faster charger, you won't have to repull the wires/cable. Just change the breaker.
 

· Registered
Joined
·
7 Posts
Discussion Starter · #6 ·
Thanks for your feedback. The CC charger has optional plugs (14-50 or 6-50). Added research on my part shows those are 4 & 3 wire respectively (I’m learning). Which way should I go?

The two-car garage is fairly small and attached. Although I don’t envision any more expansion, do you think I need a subpanel?

The Oso954 advice sounds pretty solid in light of potential future vehicles. I’m thinking the 6 Awg would be a good investment.
Thanks,
TheKingfish
 

· Registered
Joined
·
11,194 Posts
As long as you pull a 4 wire connection, H,H,N,G, you can use either receptacle and save pulling wires in the future. As your currently selected charger doesn't need the neutral, you just fold back the white if using the 6-50.

Personally, I would go with th 14-50 and connect all 4 wires in the receptacle. The plug on the charger will not have the neutral pin connected.
If some charger in the future needs the 120/240 connection it would be ready to go. If you ever have a short term use for that 120/240 connection, you can unplug the charger and plug in the other use. The 14-50 has a lot more uses than a 6-50.
 

· Registered
Joined
·
7 Posts
Discussion Starter · #8 ·
Oso954,
Your advice was extremely helpful. For max flexibility, I plan to go with the NEMA 14-50R receptacle powered by 6-3/g cable from a double-pole 50A breaker. In conjunction with that circuit, I will purchase the 32A charger with the matching 14-50 plug.
Thanks,
TheKingfish
 