Discussion Starter · #1 ·
I’m looking to add a new circuit to my electrical panel. There is plenty of space for the new breaker, but the neutral / ground bar is totally full. That’s not a big deal for the ground wire as you can have more than one ground wire to a screw. But it is a problem for the neutral as you are supposed to only have one neutral wire for one screw.

I could solve this problem by buying this little guy and mounting it to the panel box…

https://www.amazon.com/MURRAY-ECLX0...494612207&sr=8-2&keywords=murray+electric+bar

But then what?

Do I need to run a jumper from the existing ground / neutral bar to the new one? With what gauge wire? Or maybe I don’t? What then?

For reference, my electrical panel is a Cutler Hammer CH14D200 circa 1973. There is only one combo neutral / ground bar, and there are no specs on any label that describe how many wires can go with each screw. The way it is set up now, there are multiple grounds to single screws, but each neutral has its own screw.



This is not my box, but is the type of box I have.
https://www.google.com/search?q=CH6...AUICCgD&biw=1280&bih=876#imgrc=zbD7FZuwrkECVM:




Thanks!
 

·
Registered
Joined
·
10,018 Posts
dude i cant even count that high as to how many panels i have opened and saw two neutrals under one screw, its not a big deal
It not a big deal other than violating the NEC and the panel UL listing.
It doesn't matter how often you have seen hack work, doing it is not OK.

The OP should purchase and install a ground bar for his panel. Then transfer ground wires from the existing neutral bar to the new ground bar. That will free up a few positions for additional neutrals.
 

·
Registered
Joined
·
1,806 Posts
It not a big deal other than violating the NEC and the panel UL listing.
It doesn't matter how often you have seen hack work, doing it is not OK.

The OP should purchase and install a ground bar for his panel. Then transfer ground wires from the existing neutral bar to the new ground bar. That will free up a few positions for additional neutrals.
Why would they sell 40 and 42 place panels with only 20 spots on the neutral and ground bars?
 

·
Registered
Joined
·
1,806 Posts
I’m looking to add a new circuit to my electrical panel. There is plenty of space for the new breaker, but the neutral / ground bar is totally full. That’s not a big deal for the ground wire as you can have more than one ground wire to a screw. But it is a problem for the neutral as you are supposed to only have one neutral wire for one screw.

I could solve this problem by buying this little guy and mounting it to the panel box…

https://www.amazon.com/MURRAY-ECLX0...494612207&sr=8-2&keywords=murray+electric+bar

But then what?

Do I need to run a jumper from the existing ground / neutral bar to the new one? With what gauge wire? Or maybe I don’t? What then?

For reference, my electrical panel is a Cutler Hammer CH14D200 circa 1973. There is only one combo neutral / ground bar, and there are no specs on any label that describe how many wires can go with each screw. The way it is set up now, there are multiple grounds to single screws, but each neutral has its own screw.



This is not my box, but is the type of box I have.
https://www.google.com/search?q=CH6...AUICCgD&biw=1280&bih=876#imgrc=zbD7FZuwrkECVM:




Thanks!

If it's not a sub panel the neutral buss must be grounded. Not sure if a jumper is an acceptable method. Or what gauge.
 

·
Super Moderator
Joined
·
15,448 Posts
dude i cant even count that high as to how many panels i have opened and saw two neutrals under one screw, its not a big deal

and anybody with at least a few years experience who tells you they have never done that in a pinch is a liar
Find another subject to give information on because you clearly do not know the code and correct wiring methods .
 
  • Like
Reactions: brric

·
Administrator
Joined
·
41,919 Posts
This site does not promote knowingly giving bad/non code compliant advise/instructions.

Some post have been removed. Please make sure the advise or instructions you are giving, are code compliant. Thank you.
 

·
Registered
Joined
·
423 Posts
Back to the original question - (for my own knowledge) can you add another Bus bar and have it considered a Neutral/Ground bus bar with a jumper , or do neutrals all have to be connected to a common bar?
 

·
A "Handy Husband"
Joined
·
13,415 Posts
The compliant way that probably is the easiest is:

Remove several grounds from the bar, wire nut them together with a pigtail back to the neutral/ground buss. Select #14 and #12 grounds and use a #12 pigtail.

Sent from my RCT6203W46 using Tapatalk
 

·
Registered
Joined
·
1,806 Posts

·
Super Moderator
Joined
·
15,448 Posts
The bond screw or strap is used on a service panel only. It does not allow neutrals to be installed on a ground bar screw to the enclosure.
 

·
Registered
Joined
·
1,806 Posts
The bond screw or strap is used on a service panel only. It does not allow neutrals to be installed on a ground bar screw to the enclosure.

What if the ground bars and neutral bars are bonded to each other (like on a service panel) can you put neutrals on either bar?

I have a new house going up, I should look and see what the electrician did. Just out of curiosity.
 

·
Remodel and New Build GC
Joined
·
10,479 Posts
What if the ground bars and neutral bars are bonded to each other (like on a service panel) can you put neutrals on either bar?

I have a new house going up, I should look and see what the electrician did. Just out of curiosity.
As Big asks.... with maybe a #4 or 6 solid.

(I realize it's usually/probably easier to add a ground bar and move some grounds off the neutral, but it might sometimes be easier to add another neutral at a location more convenient to original wiring.)
 

·
Super Moderator
Joined
·
15,448 Posts
If an auxiliary ground bar is added it can only contain grounding conductors . No neutrals can be on a bar screwed to the enclosure .
 
  • Like
Reactions: BIG Johnson

·
Super Moderator
Joined
·
15,448 Posts
You would be putting neutral current on the metal parts of the enclosure and creating a shock hazard .
 