Discussion Starter · #1 ·
i have a 18 year old Lennox AC unit. (model number:HS18QC-211-C1P)recently The outside fan starts for a few seconds, appears to be spinning fine - with no alarming noise, but then shuts off. This recurs over and over if the AC is left on.

Here's a list of things I've tried to troubleshoot the problem:

-Measure the 24 volts AC control signal on the contactor, when outside fan starts, it has 24 volts AC, but when fan shuts off, it has 0 volts AC.


i'm out of ideas. Any help would be great. please see the attached picture if necessary.
 

Attachments

· Registered
Joined
·
7 Posts
Discussion Starter · #3 ·
Bypass DL15 delay-compressor I

I have tried to bypass DL15 delay-compressor I(see IMG_4643.JPG), the fan is ok now. Is it possible that there is sensor on the DL15 which will detect the low refrigerant please?

Or I should just need to order a new DL15 for replacement?
 

· Banned
Joined
·
3,705 Posts
I agree, probably low on freon, which means there is a leak somewhere. Not a good idea to disable safety features, might get really expensive.
His thermostat probably has a delay built into it also.

The OP mentioned jumping out the time delay. The only divination I see is he does not mention if the compressor starts too.

There is a low pressure control that will kill the compressor and fan.

The time delay is either good or bad in my experience and won't cause short cycling.

Just to test it jump out the time delay, if you are low on freon the compressor will cut on and off with the fan. If that happens you need freon.

Don't just have a tech fill it up, have him look for leaks. Very possible that you have too small a leak to find.
Luck.
 

· Registered
Joined
·
7 Posts
Discussion Starter · #6 ·
the compressor starts too.

I just do some research, it seems to me that a low pressure control is not on the DL15.

DL15 is only a time delay, am I right?

I have tested to bypass the DL15, The compressor and fan will not cut on and off. they are running ok, did I just need to order a new DL15.

By the way, so far, I don't see any leaks.
 

· Registered
Joined
·
37 Posts
i have a 18 year old Lennox AC unit. (model number:HS18QC-211-C1P)recently The outside fan starts for a few seconds, appears to be spinning fine - with no alarming noise, but then shuts off. This recurs over and over if the AC is left on.

Here's a list of things I've tried to troubleshoot the problem:

-Measure the 24 volts AC control signal on the contactor, when outside fan starts, it has 24 volts AC, but when fan shuts off, it has 0 volts AC.


i'm out of ideas. Any help would be great. please see the attached picture if necessary.
Also measure the voltage going To your fan from the contactor if measured 240 VAC and the fan motor is not spinning you have a bad fan motor. The capacitor looks OK, but to properly test your capacitor is by using a capacitor tester.
 

· Registered
Joined
·
13 Posts
What is S5 on your wiring diagram? It looks like "thermostat r---".

Do you have a steady 24 volts between Y1 and X? If this is cycling on and off the problem is with your thermostat.

Do you have a steady 24 volts between pin 1 and pin2 of the DL15 module? If this is cycling on and off, and
Y1 to X isn't, the problem is that S5 thermostat, whatever that is.

If both of those voltages are steady on, then it looks like the DL15 is bad.
 