Hey I have a split system that is not cooling. I checked the super cooling and all the numbers look good to me. Here are the numbers I'm getting:
Outside temp 97°
Suction line 90 psi 62 °
Liquid line 225 psi 103°
inside
Suction line 56°
Louid line 82.7°
Wet bulb 71°
ambient temperature in the house is 80 degrees.
the air coming out of the vents is 75
the ir temperature of the coils is 59
the air coming across the coils is 67
the air as it leaves the fan compartment entering the heating coils is 71.5
so I seem to be losing so little bit of the cold air in the vents. I would take the statue in said I would think the coils would be lower than 59 degrees.
I checked the air handler for leakage, but didn't find anything wrong. Any clues what to check next?
Thanks for the help!
Outside temp 97°
Suction line 90 psi 62 °
Liquid line 225 psi 103°
inside
Suction line 56°
Louid line 82.7°
Wet bulb 71°
ambient temperature in the house is 80 degrees.
the air coming out of the vents is 75
the ir temperature of the coils is 59
the air coming across the coils is 67
the air as it leaves the fan compartment entering the heating coils is 71.5
so I seem to be losing so little bit of the cold air in the vents. I would take the statue in said I would think the coils would be lower than 59 degrees.
I checked the air handler for leakage, but didn't find anything wrong. Any clues what to check next?
Thanks for the help!