Replacing ac compressor fan motor. Old motor was a 20+ year old GE motor with 3 wires. From the motor: Black wire went to contact relay. Purple wire went to one lead of capacitor. Brown wire went to other lead of capacitor. There was a blue striped wire that also went into one of the capacitor leads. but wasn't from the motor. New motor is Wagner 840729. Can't figure out wiring. I am thinking the two brown wires should go to the leads of the new run cap. The blue striped wire attaches to one of the cap leads. Yellow and black go into contact. Did I get this right?
 

· Registered
Joined
·
18 Posts
Discussion Starter · #3 ·
the striped wire is coming from the black box attached to the compressor. in the old configuration the wire was pigtailed to the run cap with the other end directly to line power.

also, can i attach the yellow wire to the contactor relay by the push on lug terminla or does it have to go under a screw terminal.
 

· Registered
Joined
·
18 Posts
Discussion Starter · #5 ·
Thanks for the help. Sorry to be a pest here, just want to make sure I am clear on this blue striped wire because my gut instinct is to rewire it the way it was before which would mean I would attach it to the cap. In the old and new config I am using a run capacitor just of appropriate size to drive the fan motor. Why does the blue striped wire now go to the contactor instead of the capacitor as it did in the previous config?
 

· Registered
Joined
·
18 Posts
Discussion Starter · #9 ·
i'm thinking there might be some other problem. after trying what you suggested I decided to wire similar to my original configurations....the black wire with blue stripe wired to the cap and the yellow wire to the contactor. when i did this the unit behaved just as it did before i replaced any parts. that is, the compressor sounded like it kicked on and was trying to do its thing but the fan did not run and the unit got very hot very fast. at this point i killed the power.

i do have some folks coming out to give me estimates on a new ac. this is probably a 20-30 year old system that looks to be 100% original. I was just hoping to do a quick hold me over fix until i got a new system installed. what do you think?
 

· Registered
Joined
·
18 Posts
Discussion Starter · #11 ·
Picture Key:

1. Full exterior shot.
2. Wires coming out of new fan motor. Yellow, Black, Brown, Brown Stripe
3. New fan motor capacitor. Currently wired with brown and brown stripe wire from fan motor. You can also see the blue striped wire that I have attached to the cap.
4. Shot of the 3 system capacitors.
5. Another capacitor shot.
6. Contactor relay. You can see the yellow wire from fan motor, the black wire from the fan motor (the one with the new looking red crimp connector). In this shot you can also see the pigtailed blue stripe wire.
 

Attachments

· AKA HVACTECHFW
Joined
·
2,427 Posts
You have a very old GE condenser. The black wire from the fan and the striped wire from the compressor go to opposite incoming wire as what goes to contactor. Yellow to contactor... brown and brown/white to opposite sides of new capacitor. This should get the fan running....
 

· Registered
Joined
·
18 Posts
Discussion Starter · #14 ·
OK, the good news....wired as you said in previous post....got the fan going...made me happy for a second.

the bad news....major smoke coming from the contactor relay....killed power before I burned the house down.
 

· Registered
Joined
·
18 Posts
Discussion Starter · #16 ·
yeah it just might be a sign. it's dark now so I will have to check out the damage in the morning and see what exactly got burned up. like i said this thing is old old old and I fully expect to be replacing it very soon. thanks for your help in any case.
 

· Registered
Joined
·
18 Posts
Discussion Starter · #19 ·
Turns out the fabric was covering the coil on the relay. Apparently whatever I did wiring wise yesterday smoked the coil. Brought it to the HVAC supply and said "I need one of these". Guy was like what is it. Its a contactor relay....oh I've never seen one like this, must be the first one ever made. As we already know my system is pretty much ancient. Buddy of mine came over and we figured out how to wire the new relay...used the 3 wire motor connection instead of 4. Everything is back up and running...house is cool and I am happy. Just need to get through the summer and then a modern system will be installed!
 

· Registered
Joined
·
5 Posts
Hi Folks,

I have the same issue, going from a 3 wire to 4 wire compressor fan motor. I currently have a dual cap and the motor electrical diagram shows the brown and brown/white wires both going to the cap. Can both of those wires attach to the dual cap fan leads? Each of the 3 sections of the cap has 4 leads with only one on each currently being used for the power supply, Herm, and fan sections. Can I just attach both wires to the fan section since there are 4 leads on that section sticking out? Thanks in advance.
 