Wait a minute.....there should be no potential between A to B or C to D. Those points are in line....no potential. OP should be reading volts between A to C to get 240v or B to D to get 240v.
He should also test each point to the neutral to get 120v each.

The reading he had of 118esh from C to D might indicate a short downstream on that phase. I think the breaker is doing its job and replacing it will not correct the problem.
 