Wiring a mini-split a/c and the manual says use a 14 awg & 20A breaker.
I ran about twenty feet of 14 awg exterior sheathed solid wire through conduit at the panel through the exterior wall and to the outside condenser unit.
...*then* I read "use a 20A breaker"
I thought I was going to use a 15A breaker.
Can I use a 20A breaker with this wiring?
This is the manual. See page #24 of the .pdf
http://us.lge.com/download/product/...21HNP_Service_Manual_(3828A20926C)_011607.pdf
Can this unit operate on a 15A breaker?
See page #11 (first column unit LAN091CNP / LAU091CNP)