Discussion Starter · #1 ·
I have installed a sub panel for a hot tub with a 50 Amp GFCI. The GFCI trips right away. I have removed all the load side wires and it still trips. To review how I have things hooked up after a bit of troubleshooting: The line side hots are attached to the sub panel terminals. The line neutral is tied to the neutral bar. The GFCI load neutral line is tied to the neutral bar. When the GFCI is snapped into place and the breaker set, it's trips right away. No wires are attached to the load side at all. So why does it trip?
 

· Registered
Joined
·
8 Posts
Discussion Starter · #7 ·
The GFCI pigtail is attached to the neutral bar. The kicker here is that nothing is attached as far as a load. The wiring to the hot tub isn't run yet. Alll that is there is the GFCI and the line connection. So bad GFCI?
 

· Registered
Joined
·
1,013 Posts
The line neutral is tied to the neutral bar. The GFCI load neutral line is tied to the neutral bar.
This is incorrect, the LOAD neutral should not connect to the neutral bus bar! Only the white wire attached to the GFCI should be connected to the neutral bus bar (the factory installed wire). According to the above quote, you have a short white wire attached to the LOAD Neutral and also attached to the panel neutral bus.
 

· Registered
Joined
·
8 Posts
Discussion Starter · #11 ·
Ok, I think a couple things are getting confused here.........let me try again. This is what is hooked up and where:

From the main panel in the house: I have the black and red wires (Hot Lines) attached to the line terminals on the sub box. The white wire from the main panel is attached to the neutral bar in the sub box.

The white wire, that is part of the GFCI, is attached to the neutral bar in the sub box.

No wires from the hot tub (Load lines) are attached at all to the GFCI.

I clip the GFCI into the sub box and put the lever to the "on" position and it trips right away.

Basically use the picture that 300zx posted and take the three load lines out of the picture. This is what has me confused. I have nothing attached TO the GFCI and it trips.
 

· Registered
Joined
·
8 Posts
Discussion Starter · #13 ·
Yes to both.

The ground wire from the house is now hanging free, I did have it attached to the metal case of the sub box at one time. Didn't matter either way.

The neutral bus on the sub box is isolated from the box.
 

· Registered
Joined
·
8 Posts
Discussion Starter · #15 ·
300zx......hooking the ground wire to an isolated bar is going to help what? I'm missing something here.

Is the ground and the neutral supposed to be hooked together at the house box? Are they supposed to be separate from the other neutral and grounds in there?
 

· Banned
Joined
·
5,990 Posts
You could run just hot and neutral jumper wires to the line side of the unmounted GFCI, with nothing on the load side. If it trips it almost certainly is bad.

Then add the ground wire and see what happens.

If it works so far add wiring to the load side.

If it still works add the load.

Divide and conquer.
 

· Registered
Joined
·
8 Posts
Discussion Starter · #18 ·
jerryh3, that is the conclusion I came to but thought I'd better check and see if I did something stupid here. I plan on exchanging the GFCI on my way home today. If that doesn't work, I'll certainly take pictured and palsture them up to get experts input.
 