Good morning I have a really quick question for you, I recently purchased a delta 46-460 midi lathe two weeks ago and last night I was sinning a bowl 8 inches in diameter. when I give it pressure the bowl slowed down almost to a stop. I am concerned that it might be the motor or is this normal? I could really use your help I just starting learning to spin and I feel in love with it and the machine.
 

·
Registered
Joined
·
37,261 Posts
Just some guesses.
Dull chisle.
Trying to make to deep a cut.
Trying to us it with a long under sized extention cord.
Using a 15 amp circut.
Trying to run it where there was to small a wiring feeding the circut.
 
  • Like
Reactions: Cricket11b30

·
Registered
Joined
·
8 Posts
Discussion Starter #3
Thank you I will give all those a try I think I need to change the breaker anyway because I keep tripping the same one with my miter saw.
 

·
Registered
Joined
·
37,261 Posts
Where are you trying to run the lathe?
Time and time again I see DIY's running way to small a wire to a shed or garage thinking I only need one outlet and a light and want to save money then end up adding stuff one and have it not working.
 
  • Like
Reactions: Cricket11b30

·
Registered
Joined
·
8 Posts
Discussion Starter #5
I am running it in the garage, The garage is attached to the house so there is no shady wiring running from point A to point B. I just recently I started trip the breaker it never happened before I I am going to run out in a few to lowes and purchase a stronger breaker and change it, out like you suggested hopefully that will help.
 

·
Super Moderator
Joined
·
9,090 Posts
You just can't buy a stronger breaker.
The breaker has to be sized for the wire, so if you #14, then you can only install a 15 amp breaker.
 

·
Registered
Joined
·
37,261 Posts
Hold on, what sized wire is running to that circut?
If it's 14-2 you can only have a 15 amp.breaker.
If it's 12-2 you can use a 20 amp breaker.
Using to high an amperage breaker and the wires can melt before the breaker ever trips.
 
  • Like
Reactions: Cricket11b30

·
Registered
Joined
·
8 Posts
Discussion Starter #8
joecaption said:
Hold on, what sized wire is running to that circut?
If it's 14-2 you can only have a 15 amp.breaker.
If it's 12-2 you can use a 20 amp breaker.
Using to high an amperage breaker and the wires can melt before the breaker ever trips.


image-455286649.jpg

Ok this is what's have bare with me I am just a little drill sergeant not very skilled like you guys just enjoy doing things my self with a little help
 

·
Registered
Joined
·
8 Posts
Discussion Starter #9
joecaption said:
Hold on, what sized wire is running to that circut?
If it's 14-2 you can only have a 15 amp.breaker.
If it's 12-2 you can use a 20 amp breaker.
Using to high an amperage breaker and the wires can melt before the breaker ever trips.
I sent a pick I was wondering if you could give me your best suggestion

image-2240907008.jpg
 

·
Super Moderator
Joined
·
9,090 Posts
Permission to recover drill sgt?

You have 20 amp breakers and can't exceed that size.
You need to find out why the breaker is tripping.
 

·
Registered
Joined
·
8 Posts
Discussion Starter #11
jbfan said:
Permission to recover drill sgt?

You have 20 amp breakers and can't exceed that size.
You need to find out why the breaker is tripping.
To funny lol so do ou think it would be a good idea to just replace with the same size
 

·
Super Moderator
Joined
·
9,090 Posts
You don't have a choice but to change it for the same size.
They are cheap enough, but it may not be the problem.
 

·
Registered
Joined
·
8 Posts
Discussion Starter #13
jbfan said:
You don't have a choice but to change it for the same size.
They are cheap enough, but it may not be the problem.
Because it just started doing when I starting put my wood shop to get her and it only does it when I use my miter saw and once when I used my table saw
 

·
Super Moderator
Joined
·
9,090 Posts
You need to check the circuit for a loose connection from the panel to all the receptacles.
You should also check you saw on another circuit to make sure that is not the problem.
 

·
Registered
Joined
·
8 Posts
Discussion Starter #15
jbfan said:
You need to check the circuit for a loose connection from the panel to all the receptacles.
You should also check you saw on another circuit to make sure that is not the problem.
Will do thank you
 