Discussion Starter · #1 ·
Good morning I have a really quick question for you, I recently purchased a delta 46-460 midi lathe two weeks ago and last night I was sinning a bowl 8 inches in diameter. when I give it pressure the bowl slowed down almost to a stop. I am concerned that it might be the motor or is this normal? I could really use your help I just starting learning to spin and I feel in love with it and the machine.
 

· Registered
Joined
·
37,499 Posts
Just some guesses.
Dull chisle.
Trying to make to deep a cut.
Trying to us it with a long under sized extention cord.
Using a 15 amp circut.
Trying to run it where there was to small a wiring feeding the circut.
 
  • Like
Reactions: Cricket11b30

· Registered
Joined
·
37,499 Posts
Where are you trying to run the lathe?
Time and time again I see DIY's running way to small a wire to a shed or garage thinking I only need one outlet and a light and want to save money then end up adding stuff one and have it not working.
 
  • Like
Reactions: Cricket11b30

· Registered
Joined
·
8 Posts
Discussion Starter · #5 ·
I am running it in the garage, The garage is attached to the house so there is no shady wiring running from point A to point B. I just recently I started trip the breaker it never happened before I I am going to run out in a few to lowes and purchase a stronger breaker and change it, out like you suggested hopefully that will help.
 

· Super Moderator
Joined
·
11,035 Posts
You just can't buy a stronger breaker.
The breaker has to be sized for the wire, so if you #14, then you can only install a 15 amp breaker.
 

· Registered
Joined
·
37,499 Posts
Hold on, what sized wire is running to that circut?
If it's 14-2 you can only have a 15 amp.breaker.
If it's 12-2 you can use a 20 amp breaker.
Using to high an amperage breaker and the wires can melt before the breaker ever trips.
 
  • Like
Reactions: Cricket11b30

· Registered
Joined
·
8 Posts
Discussion Starter · #8 ·
joecaption said:
Hold on, what sized wire is running to that circut?
If it's 14-2 you can only have a 15 amp.breaker.
If it's 12-2 you can use a 20 amp breaker.
Using to high an amperage breaker and the wires can melt before the breaker ever trips.


Technology Metal


Ok this is what's have bare with me I am just a little drill sergeant not very skilled like you guys just enjoy doing things my self with a little help
 

· Registered
Joined
·
8 Posts
Discussion Starter · #9 ·
joecaption said:
Hold on, what sized wire is running to that circut?
If it's 14-2 you can only have a 15 amp.breaker.
If it's 12-2 you can use a 20 amp breaker.
Using to high an amperage breaker and the wires can melt before the breaker ever trips.
I sent a pick I was wondering if you could give me your best suggestion

Technology Metal
 

· Super Moderator
Joined
·
11,035 Posts
Permission to recover drill sgt?

You have 20 amp breakers and can't exceed that size.
You need to find out why the breaker is tripping.
 

· Registered
Joined
·
8 Posts
Discussion Starter · #13 ·
jbfan said:
You don't have a choice but to change it for the same size.
They are cheap enough, but it may not be the problem.
Because it just started doing when I starting put my wood shop to get her and it only does it when I use my miter saw and once when I used my table saw
 

· Super Moderator
Joined
·
11,035 Posts
You need to check the circuit for a loose connection from the panel to all the receptacles.
You should also check you saw on another circuit to make sure that is not the problem.
 
1 - 15 of 15 Posts