Can someone verify my thinking. I have a 400 amp service run is <100'
1- 4/0 triplex should be enough for the max rating no?
1- 4/0 triplex should be enough for the max rating no?
Attachments
-
1.4 MB Views: 505
-
1.2 MB Views: 355
Heck no. 4/0 Aluminum is only rated for 180 ampsCan someone verify my thinking. I have a 400 amp service run is <100'
1- 4/0 triplex should be enough for the max rating no?
It's not in free air. The free air rating is for individual wires. Since this is triplex, it's a cable and it doesn't apply.4/0 THHN on a messenger in free air rated at 224 amps.
Yes and this why I'm second guessing the licensed electrician that I hired. The inspector told me they need to be on one lug.No. Violations on you feeder terminations as well.
Ok now I'm learning a bit more. I don't know where to get into and out of the tables. But this helps. Thank you!It's not in free air. The free air rating is for individual wires. Since this is triplex, it's a cable and it doesn't apply.
Service wires and feeder are required to be 83% of the rating of the service.So do I need to buy two 4/0 tri-plex?
No, no, no! You can't "just up-and decide to parallel". Since you are under NEC, paralleling requires a bunch of factors, including special equipment on the source side. Don't even dream of taking it on as an amateur, and the essential ingredient is a special cabinet rated for paralleling at the source.Yes and this why I'm second guessing the licensed electrician that I hired. The inspector told me they need to be on one lug.
So do I need to buy two 4/0 tri-plex?
Only in NEC land. Power companies follow NESC. Totally different. Like French and German.Service wires and feeder are required to be 83% of the rating of the service.
Yes, that's why I am out of my element. I am supplying the material and the electrician will be here on Sunday. At this point I am second guessing everything he says because it has been contradicted by others.Usually the POCO is responsible up to the meter. Are there special circumstances here?
Thank you and to everyone else.Dual 4/0 per phase will work for 400 amp.
Normally it is not my concern. In this case it is. I am supplying the material labor and ditch from the meter to the pedestal. Trust me, I prefer that I didn't.So exactly is this situation? Are you talking about the service drop from the POCO source to their meter? If so, why is it your concern or responsibility?