Installing 4 ceiling lights and would like to have control of them through 3 different switch locations. I'm confused on how to wire, I have 12/2 wire coming into the primary switch box and so I need help with how to get the other two switch locations tied to the lights.
 

· Super Moderator
Joined
·
24,944 Posts
Run power into first switch.
Run 12/3 wires from the first switch to the second switch and then to the third switch.
Run 12/2 cable from the third switch to light one then light two etc.
 

· Registered
Joined
·
13 Posts
Discussion Starter · #3 ·
Run power into first switch.
Run 12/3 wires from the first switch to the second switch and then to the third switch.
Run 12/2 cable from the third switch to light one then light two etc.
Great start....couple of more -

1. (Switch 1 to Switch 2 then Switch 2 to Switch 3) OR (Switch 1 to Switch 2 then Switch 1 to Switch 3)

2. Can the 12/2 (for the lights) start at any of the switches or does it have start from the last switch (#3) in the run of power from the first switch?

Thanks :thumbsup:
 

· Registered
Joined
·
2,797 Posts
Installing 4 ceiling lights and would like to have control of them through 3 different switch locations. I'm confused on how to wire, I have 12/2 wire coming into the primary switch box and so I need help with how to get the other two switch locations tied to the lights.
You will need two 3-way switches and one 4-way switch. Power comes into one of trhe 3-way location(in diagram below this is the left 3-way). The 4-way switch is wired between the two 3-ways. The 3-way on the right in the diagram is taking the switched power to the lights.

The 3-way location on the right in the diagram may require a neutral at the location depending on your code. The switch itself does not need the neutral to function but newer codes require a neutral at all switch locations.

Also no ground wires shown for ease of drawing.
 

Attachments

· Registered
Joined
·
2,797 Posts
Thats a code violation. Go from s1-s2-s3 then to lights to keep nuetral at everyswitch location
Depending on his current wiring setup...DAMN the neutral at the far right switch location in the above diagram. If the poster is never going to automate or use sensing switches...DAMn the neutral.:thumbup::thumbup:
 

· Licensed Electrician
Joined
·
4,352 Posts
I will argue that a dead end three-way/four-way does not require a neutral since it is a switch loop.


404.2 Switch Connections.
(A) Three-Way and Four-Way Switches. Three-way and
four-way switches shall be wired so that all switching is
done only in the ungrounded circuit conductor. Where in
metal raceways or metal-armored cables, wiring between
switches and outlets shall be in accordance with 300.20(A).

Exception: Switch loops shall not require a grounded
conductor.
 
  • Like
Reactions: Speedy Petey

· Super Moderator
Joined
·
18,302 Posts
I will argue that a dead end three-way/four-way does not require a neutral since it is a switch loop.
Interesting because (C) seems to contradict the exception to (A). The inspectors and professional forums all talk about needing the neutral, regardless, including the death of a dead end three way.
 

· Licensed Electrician
Joined
·
4,352 Posts
Interesting because (C) seems to contradict the exception to (A). The inspectors and professional forums all talk about needing the neutral, regardless, including the death of a dead end three way.

THB, we are still on 2008 so I don't know the ins and outs of it, but the way I read it, neutrals are not needed at dead ended 3/4 ways.

What I find a little curious, is why switch loops is in 3/4 ways, when it is just as, if not more, common to have a switch loop for a single pole.
 

· Registered
Joined
·
10,386 Posts
Not all boxes in 3 way and 4 way switch loops have raw hot so neutral would
be of limited or no value.
 

· Registered
Joined
·
13 Posts
Discussion Starter · #16 ·
If the circuit in the diagrams has four lights at 100W I calculated the current at 100W*4/110V = ~3.5A, correct?

And if correct is there any reason why I can't run 14/3 wire through the switches and 14/2 from the last switch to the lights?
 