I bought a construction heater that is 30 amp 240 volt. I bought a special receptacle for it and a 30 amp double pole breaker. I used #10-2 wire. I connected the black to one side of the breaker and the white to the other side. This didn't leave me a neutral wire. Now when I turn the breaker on it trips off right away. What have I done wrong??
Thanks,
Blaine
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts
Agree. it sounds like you wired the breaker side correctly.

What did you do with the white wire at the heater receptacle? The receptacle should not have had a place for a neutral.
 