1 - 6 of 6 Posts
Hi,
I've looked around a good bit to find this answer, but not really anything that fits this scenario.
Currently building a media room. Had to buy a new ceiling fan that is flush mount to make room for projector line of sight, which is also ceiling mounted. But had to remove the ceiling fan light. Instead I will have three 5-foot tall Asian style lamps around the room for ambient lighting when needed. I would like for these to be controlled by a light switch near the entrance to the room. Since 2 of the outlets these lamps plug into also share power with the subwoofers for the room, I thought half hot outlets would make sense.
So the power is sourced at the outlets and they are daisy chained around the room. So the 3 outlets that I want half hot and switched do have other outlets in between that would not be half hot or switched. It's all 14/2 wire and a 15 amp circuit.
In my head I would run 14/3 wire from the switch to each of the 3 outlets, doing a switch loop at each outlet, breaking the hot tab on each, and congregating all 3 wires into a common pool at the switch. Something like this....
See attached - Drew this in paintbrush in the same style that I see a bunch of other diagrams in google search...
Is this how this should work? I'm ok with electrical stuff, but I like to figure things out and spend time on it in my head before I dive in. I would like some concurrence on the solution though...or a better way. That is always helpful.
Thanks for your time.
Jason
Super Moderator
Remove the two right '2 wire cables'.
One 14/3 between the receptacles is all you need. Use the red wire on the receptacle 1/2s you want switched and the black on the unswitched ones.
I believe that what you have proposed is much more complex than is necessary.
As joed said!
Below is a simplified diagram of what is required (Grounds, connectors and pigtails have been omitted for clarity.)
Three half switched receptacles are shown with a non-switched pair of receptacles between each pair of half switched receptacles.
"One 14/3 between the receptacles is all you need" plus one 14/2 from one (any) receptacle to the switch.
Discussion Starter #4
Ahh thanks so much for responding. Yes that is much easier. I would definitely do that if I were running it brand new. I feel I left out a key component. The 14/2 wire between all the outlets is existing. So I was looking for something new I could add to make 3 of the outlets half hot without running all new wire to all of the outlets. There are about 8 outlets around the room but only 3 of them need to be half hot switched.
Due to their location, it is actually less wire to run it directly to each of the 3 versus around the entire room hitting each outlet. One of the 3 switched ones is at the end of the existing 14/2 run, but coincidently very close to the where the switch would be.
Updated the diagram to show what is existing and what would be new...
Thanks
Jason
Leaving the existing wiring and breaking the "hot" tabs where required, you really need only one conductor to the switch (from the Line connection at any non-switched half receptacle) and one conductor from the switch to the other (switched) half receptacle - and then on to the other two switched half receptacles.
You would need only to run 14/2 cable. (The "Neutral" conductor in this new cable to the latter two receptacles is not needed and should be "capped" appropriately.)
1 - 6 of 6 Posts