Discussion Starter · #1 ·
I hope I'm posting this in the right area.I appreciate any input as I have no knowledge in electrical.I have a concrete floor grinder that requires 220v to run.My plan was to hook it up to my 5500 watt generator in the 120/240v outlet.My dilemma is that the plug on the machine is a 3 blade and the the generator takes a 4 blade connector.Can I swap the plugs out ? If so what wires go where? thanks for any help...
 

· Registered
Joined
·
4 Posts
Discussion Starter · #3 ·
Thanks for the reply, so just to make sure I understand..Im going to use the 3 wires off the 3 blade connector and connect them to the L14-30P cap,so ill have a ground wire and the other 2 wires connected to the new cap but not using the neutral at all? Does that make sense..

Lastly what blades does the wires hook up to on the new cap, I know one blade has a L shape to it...

thanks for your help
 

· Electrical Enthusiast
Joined
·
729 Posts
Lastly what blades does the wires hook up to on the new cap, I know one blade has a L shape to it...

thanks for your help[/QUOTE]

The L-shaped one is the ground connection, it should be a bare or green-colored wire.
The two prongs to the left and right of this are your two hot connections, the other two wires will connect to this. The prong across from the ground (L-shaped) prong would be the neutral, which you aren't using in this case. :thumbsup:
 

· Registered
Joined
·
756 Posts
The L-shaped one is the ground connection, it should be a bare or green-colored wire.
The two prongs to the left and right of this are your two hot connections, the other two wires will connect to this. The prong across from the ground (L-shaped) prong would be the neutral, which you aren't using in this case. :thumbsup:
You got that dead wrong.

Mark
 

· Electrical Contractor
Joined
·
1,995 Posts
With an L14-30 plug the two hots go on the brass screws and the ground goes to the green screw. Leave the silver neutral screw empty.
 

· Registered
Joined
·
756 Posts
I'm sorry. The OP wasn't clear. Does the generator have a locking receptacle or not. My comment was directed at non-locking. I don't know that I would say the blade on a locking plug is exactly "L" shaped.

I missed the second OP post that specified locking.

Mark
 