Small 70x12, 3/12 pitch roof, summer home in ocean city, md.
6" soffit vent. And gable vents and 2 roof vents.

What batts insulation do you recommend?
 

·
Registered
Joined
·
104 Posts
Discussion Starter #3
I haven't done the soffit yet plan was to vent the entire soffit and put the baffle shoots.
I know blown insulation is possible but batts is easier for me at this time. Just wondering what batts I should use, r-38 faced down.
 

·
Exterior Construction
Joined
·
26,145 Posts
Air Seal the attic floor at all the top plates and penetrations.

At that point, facing on the FG (as long as you have drywall that is air tight and has at least 2 layers of paint) is not required.

If you do put it in there with facing, facing goes towards the drywall.
 

·
Registered
Joined
·
104 Posts
Discussion Starter #5
Thanks, I know not required just asking what you would do. I want to make it warm/cool according to season but not sure what r value I should use?
 

·
Registered User
Joined
·
11,730 Posts
Energy code requires R-38, minimum; http://energycode.pnl.gov/EnergyCodeReqs/index.jsp?state=Maryland

You are under IRC; http://www.reedconstructiondata.com/building-codes/maryland/

Facing is required as an alternative to ventilation locations;http://publicecodes.cyberregs.com/icod/irc/2009/icod_irc_2009_8_par091.htm

--unless special vapor barrier paint is used--, two or three coats of regular paint won't meet minimum code to reduce your attic ventilation requirements. Sorry, WoW, wrong class; http://publicecodes.cyberregs.com/icod/irc/2009/icod_irc_2009_6_par006.htm

Using R-38 faced or unfaced, I would still add a housewrap over the insulation after air-sealing the attic, to prevent wind-washing in that low density batt insulation; Post #10; http://www.diychatroom.com/f103/width-insulation-rolls-196864/

IMO, use some rigid foam board at the exterior perimeter, in fact- forget the baffles altogether, make them using FB also; pp.5, "Site-built baffles"; http://www.buildingscience.com/documents/published-articles/pa-crash-course-in-roof-venting

FB on wall plates, with safety note on using it for fire-prevention;http://bct.eco.umass.edu/publications/by-title/reroofing-and-residing-to-save-energy/

Gary
 

·
Exterior Construction
Joined
·
26,145 Posts
I was not comparing kraft facing to paint. I was saying it isn't required in their case if they have painted drywall.

Home is not likely used much in the winter and there are prevailing winds.

If no mold or mildew is noted yet, it will be exponentially less likely after air sealing and additional insulation.

At just over 840 sq/ft, the only require 5.6 sq/ft or 800 sq/in of NFA.

Depending on the vent size, they may already have that.
 

·
Registered User
Joined
·
11,730 Posts
"At that point, facing on the FG (as long as you have drywall that is air tight and has at least 2 layers of paint) is not required.'----------- regular paint (Class 3)-- (unless it is a special low-perm vapor retarder/barrier paint -Class 2) has no value whatsoever as a vapor retarder per codes- to meet the ventilation rate. As that 4th link stated;


"R601.3.2 Material vapor retarder class. The vapor retarder class shall be based on the manufacturer's certified testing or a tested assembly.

The following shall be deemed to meet the class specified:

Class I: Sheet polyethylene, unperforated aluminum foil.

Class II: Kraft-faced fiberglass batts.

Class III: Latex or enamel paint."


So to meet code; either have vents (high/low)-- and sounds like you have-- per code OR faced batts for the 1/300, otherwise you need 1/150 as WoW figured for you. " As an alternative, the net free cross-ventilation area may be reduced to 1/300 when a Class I or II vapor retarder is installed on the warm-in-winter side of the ceiling."

Gary

PS. Just trying to show readers that regular paint won't meet the code requirements, only special low-perm paint.
 

·
Exterior Construction
Joined
·
26,145 Posts
Good enough and I know your aim is to educate and you do that amazing well.

I was speaking specifically to his situation and the lack of more than Class III vapor retarder given his ventilation schedule.

I would also point out that, and you know this as well, that air leaks carry exponentially more moisture than diffusion and the code is antiquated in that regard.

I would rather have a tight ceiling plane with a Class III than a bunch of can lights with a Class II. I will give you one guess as to which one will show mold and mildew in that case.
 