Discussion Starter · #1 ·
Hi guys,

When you have a 2 story house is it normal practice to just have a secondary waste vent stack that serves the 2nd story rather than having to re-vent the 1st story fixtures to a point at least 6 inches above the 2nd story fixtures and meet up with the main stack?
 

· Registered
Joined
·
2,797 Posts
Hi guys,

When you have a 2 story house is it normal practice to just have a secondary waste vent stack that serves the 2nd story rather than having to re-vent the 1st story fixtures to a point at least 6 inches above the 2nd story fixtures and meet up with the main stack?
Depending on the carpentry/wall-layout of the 2nd floor in relation to the fixture groups on the 1st floor...No
 

· Premium Member
Joined
·
13,105 Posts
So, you would rather re-vent the fixtures from first floor to extended above second floor and meet up with main stack in lets say the attic?
The only reason to do this is to minimize roof penetrations. From a contractors perspective (material & labor) it's much easier to punch a pipe through the roof then crawl around in an attic tying pipes together
 

· Banned
Joined
·
139 Posts
Discussion Starter · #5 ·
The only reason to do this is to minimize roof penetrations. From a contractors perspective (material & labor) it's much easier to punch a pipe through the roof then crawl around in an attic tying pipes together
ok so basically you would have a separate waste and vent for the 2nd story? When you run the separate vent from roof to the basement you just tie that new stack into the main drain or do you tie into the main stack rather than digging up the floor?
 

· Premium Member
Joined
·
13,105 Posts
ok so basically you would have a separate waste and vent for the 2nd story? When you run the separate vent from roof to the basement you just tie that new stack into the main drain or do you tie into the main stack rather than digging up the floor?
You don't have to have a separate w&v stacks for the 2nd floor
A vent is ran from the fixture it serves to a common vent or is ran by itself- such as many kitchen sinks are.
As long as they are sized properly- drains from different floors can tie together at any point.
As always- there are exceptions to rules...
What exactly are you trying to do anyways?
 

· Banned
Joined
·
139 Posts
Discussion Starter · #7 ·
You don't have to have a separate w&v stacks for the 2nd floor
A vent is ran from the fixture it serves to a common vent or is ran by itself- such as many kitchen sinks are.
As long as they are sized properly- drains from different floors can tie together at any point.
As always- there are exceptions to rules...
What exactly are you trying to do anyways?
Just curious because I am just starting school I hope you dont mind the questions. I know you don't need separate w/v stacks for 2nd floor but you mentioned its easier just to run one through the roof rather than tie into the main stack. Now if you don't do that then your first floor fixtures are going to have tie into the common vent stack at a point 6 inches above the highest fixtures on the 2nd floor, right? When you say it can be ran by itself like many kitchen sinks are what do you mean exactly? Thanks.
 

· Premium Member
Joined
·
13,105 Posts
Ask all the questions you want :thumbsup: There are a handful of plumbers on here regularly- from across the country. You'll soon realize that we all work under different codes. Where are you located? Do you know what code you'll be studying?
And yes, vents tie together 6" above the flood rim. Imagine bathrooms at opposite ends of a house and on separate floors. You could bring the vents together at some point or take them out as two separate vent stakes. Same goes for the kitchen. In my area, kitchens often are vented through the roof by itself because they're not close to other plumbing fixtures
 

· Master Plumber
Joined
·
1,779 Posts
Just curious because I am just starting school I hope you dont mind the questions. I know you don't need separate w/v stacks for 2nd floor but you mentioned its easier just to run one through the roof rather than tie into the main stack. Now if you don't do that then your first floor fixtures are going to have tie into the common vent stack at a point 6 inches above the highest fixtures on the 2nd floor, right? When you say it can be ran by itself like many kitchen sinks are what do you mean exactly? Thanks.
As E mentions multiple codes multiple set ups, what he means is that kitchens are usually at one end of the house and bathrooms groups are more commonly closer, you would not want to run 40 feet of pipe through the attic to vent a kitchen or bath to a common vent, and you do have limits on the travel on a re vent.
 