So to this point I've read just about everything on 240v, 3 prong wiring and I'm still stuck.

I bought a 240v, 4800w 20amp garage heater. I added the 30amp circuit (noted on the box as the required circuit), ran the 10/2 wire (it happens to be 10 CU 2, if that makes a difference, I was told it didn't), connected the 6-30p outlet, tested L1-ground, and L2-ground, each at 120v and...... the heater doesn't work.


I'm sure I'm missing something tremendously simple, but it's completely evading me.
 

·
Wire Chewer
Joined
·
3,599 Posts
Remove the breaker and make sure that it's a on using both busses. I had to shift a few breakers around in my panel to get a DP breaker to use both busses. Your panel might be arranged the same way.

To rule out a connection issue down the line test the two hots right at the breaker (be cautious while you have the cover removed while it's live).

edit: and also test at the plug, never even took into consideration it might be the heater itself.
 