Hello,

I was wondering if I could add another outlet for my dryer (250v) from the j box that is powering my stove (240v). The breaker is a duel 40amp and the wire is a 6-3g. Can I add another outlet for my dryer and simultaneously run the stove?

thanx for the help! :thumbup:
 

· E2 Electrician
Joined
·
5,656 Posts
Hello,

I was wondering if I could add another outlet for my dryer (250v) from the j box that is powering my stove (240v). The breaker is a duel 40amp and the wire is a 6-3g. Can I add another outlet for my dryer and simultaneously run the stove?

thanx for the help! :thumbup:
It would be easier to pull another branch circuit for the dryer.
 

· Registered
Joined
·
17 Posts
Discussion Starter · #3 ·
The laundry room is on the other side of the wall where the stove is. I would run another line but the breaker box is on the other side of the house and in the basement. Wanted to avoid running another line if I could.
 

· Licensed Electrician
Joined
·
4,352 Posts
I know Stick is going to argue, but I am going to say flat out that you cannot do that. The dryer will spec it be on a 30A circuit and you must follow manufacturer specifications.
 
  • Like
Reactions: jbfan

· E2 Electrician
Joined
·
5,656 Posts
I know Stick is going to argue, but I am going to say flat out that you cannot do that. The dryer will spec it be on a 30A circuit and you must follow manufacturer specifications.
Not really argue, my point was he could install a subpanel and refeed the range and the dryer off the subpanel. But as i stated, easier to run a new branch circuit.
 

· " Euro " electrician
Joined
·
5,369 Posts
Hello,

I was wondering if I could add another outlet for my dryer (250v) from the j box that is powering my stove (240v). The breaker is a duel 40amp and the wire is a 6-3g. Can I add another outlet for my dryer and simultaneously run the stove?

thanx for the help! :thumbup:
Short et sweet the answer is no you can not do this.

The dryer do required 30 amp circuit while the stove typically use either 40 or 50 amp circuit depending on conductor size.

I rather run this with new circuit for the dryer and leave the stove circuit alone.


Merci,
Marc
 

· Registered
Joined
·
10,401 Posts
If the dryer takes 30 amps and the stove takes 40 amps, you may not run a single 70 amp circuit directly to receptacles for the two of them.

The maximum circuit amperes rating for each piece of equipment, or an appliance, is stated on its nameplate, stated in the instructions, and/or implied by the size and shape of the power plug.
 