I would like to run 240v to my garage. The plan is to install a sub-panel, inside the house where the A/C #8 wire exits.

Will a sub-panel support the A/C compressor and 240v to the garage?

Note: Currently the detached garage is fed by a 30A fuse (120v), ran through buried conduit.

http://imgur.com/D3HVRFq - Service Panel Make/Type
http://imgur.com/wkNU8hy - Service Panel Wiring


P.S. I did not think that I could justify starting a new thread when, seemingly, such a similar one already existed. I apologize for any inconvenience.
 

·
Registered
Joined
·
1,324 Posts
I would like to run 240v to my garage. The plan is to install a sub-panel, inside the house where the A/C #8 wire exits.

Will a sub-panel support the A/C compressor and 240v to the garage?

Note: Currently the detached garage is fed by a 30A fuse (120v), ran through buried conduit.

http://imgur.com/D3HVRFq - Service Panel Make/Type
http://imgur.com/wkNU8hy - Service Panel Wiring


P.S. I did not think that I could justify starting a new thread when, seemingly, such a similar one already existed. I apologize for any inconvenience.
Please do start a new thread for the benefit of the Original poster, and others.
 

·
Administrator
Joined
·
40,357 Posts
Made this its own thread. So no confuses you and the OP if the OP has more questions.
 
  • Like
Reactions: dasbinder

·
Administrator
Joined
·
40,357 Posts
Already done.
 
  • Like
Reactions: dasbinder

·
Super Moderator
Joined
·
14,020 Posts
Two problems, the A/C needs its own circuit and there is no neutral in the circuit either. You are going to need to run a new circuit.
 

·
Registered
Joined
·
4 Posts
Discussion Starter #7
Two problems, the A/C needs its own circuit and there is no neutral in the circuit either. You are going to need to run a new circuit.
I updated the image from inside the panel ... http://imgur.com/IL4EAqA

My fuse diagram from when the AC was added, shows this 25A circuit for A/C and Furnace. The 'Range' used to be a an electric dryer, before it was used for the A/C ... http://imgur.com/9sZfgci
 