Discussion Starter · #1 ·
I have a water well pump that is 220v, can I come off the well connection with maybe a step down transformer to 110v to run a light in the well house and maybe a light in the shed next to the well house? the well pump pulls 2.5amps, and its on a 30 amp breaker on the outside of the house. not sure if that makes a diff or not. Thanks
 

· Electrical Contractor
Joined
·
3,370 Posts
What type of wire runs to the well house? Size of and number of conductor?

If you have the proper cable there, a simple sub-panel should do the trick without the need for a transformer.

Also, where is the pressure switch located?
 

· 2 fingered typer
Joined
·
33 Posts
I'd like to see a well pump that pulls 2.5 amps?

I have a water well pump that is 220v, can I come off the well connection with maybe a step down transformer to 110v to run a light in the well house and maybe a light in the shed next to the well house? the well pump pulls 2.5amps, and its on a 30 amp breaker on the outside of the house. not sure if that makes a diff or not. Thanks
That's less than 1/4 HP? Are you sure?
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts
If it is like 99.9% of the wells I have seen it is fed with only a 2-wire. If it is newer, or if you are lucky, it will have a ground. A neutral is highly unlikely.

I am also wondering what size wire is feeding this well. WHY is there a 30A breaker if the load is only < 3A?
 

· Registered
Joined
·
2 Posts
Discussion Starter · #5 ·
The pressure switch is located on the front of the tank, very easy to get too. its a brand new set up, about a year old. I'll have to double check the amps for the pump and the wiring tommorow.
 

· Registered
Joined
·
2,294 Posts
The main thing to check is the wiring type and size.

If you have a three wire system that has two hots, a neutral and a ground (wire or conduit), you can probably set a small sub panel and get both 120 and 240 volts out there.
 

· Registered
Joined
·
6,036 Posts
Even if you only have 2 wires I think you can put in a subpanel and put in a 230v bulb.
http://www.grainger.com/Grainger/items/1E243
Tell me if I'm wrong.
Yes, they do make 230 volt bulbs. And yes, a 230 volt bulb requires no neutral. But the motor circuit is a dedicated circuit and I am not certain about a splice for the lamp holder on this circuit. Someone can explain further. I am not sure how this could be done correctly, but yes you are correct, it can be done. But is it compliant? Thats the question. I am asking? Others?
 

· Idiot Emeritus
Joined
·
1,910 Posts
A lot of fluorescent fixtures these days have multi-volt ballasts. They will operate on any voltage from 120 to 277. The neutral doesn't need to be grounded.

The older core-and-coils 277 volt ballasts will operate on 240, but the lamps won't last as long, and they won't start as well when it's cold.

There's nothing in the code, that I know of, that says you can't have a 240 volt fixture.

Rob
 

· Banned
Joined
·
2,487 Posts
The only thing I can think of that would prevent a 240 V light in this instance would be the 30 A circuit. In residences (and I would think a pump house counts as part of the residence), 30 A circuits are not allowed to supply light fixtures.

If you changed the breaker to 20 A, or installed a subpanel at the pump, and used a 2-pole switch for the light, you would be good to go. Also, I would put a big label on the light and switch. Something like:

"WARNING: 240 Volts.
 

· Registered
Joined
·
1,013 Posts
I would think a subpanel in the well house would be fine, but as soon as you have light out there you're going to want outlets for a battery charger or something else in the shed. I would look into the 120 volt route verses the 230/240 volt route, it will be much better in the long run and provide for a lot more flexibility in the future.
 