i'm going to be buying a welder soon and i need to run a 220 volt out let off my main panel (in the garage) out let will be below the main panel.

i under stand 220 wirering some what my question my main panel only hase one space left can i use a Tandem Breaker breaker in this spot for 220.

the breaker looks like this


can it be done? i think so... fill in the gray area for me
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts
That is a twin/tandem/skinny breaker, not a two-pole breaker. That breaker will NOT give you 240v. It will give you two 120v circuits.
You need TWO spaces for a 240v circuit.

IF, and only if, your panel will accept twin breakers you can use one to free up a space in your panel by consolidating two 120v circuits to one space. Even this has risks so be sure you know what you are doing first.
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts
Also, what size circuit do you need? "220" means nothing without more info.

The circuit you need will be 240v at a certain amperage. The amperage is the size of the circuit.
 

· Registered
Joined
·
14 Posts
Discussion Starter · #10 ·
what does the two pole do that makes it 240volts that cant be acomplished with he tandem (just want ot under stand) and my box almost has all tandem breakers except for two Arc-Fault Circuit Interrupters . and 4 240v double pole
 