I just bought a 2 unit home..but....found there is only one 200 amp meter and electrical panel... I want to keep the main unit (1000sq.ft)downstairs on the 200 amp panel (where I will live), and the second unit upstairs a 100 amp panel since its smaller 700sq.ft.
Do i need a 200 amp double meter? What size service feeder? and disconnects???? HELP!!
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
In many places you can simply add a 100A service right next to the existing one.

Are you doing this or will you hire an electrician? What is your level of expertise?
 

·
Registered
Joined
·
5 Posts
Discussion Starter · #3 ·
I've done electrical work in the past and can change service.... the electic company says the meter has to be moved to the other side of the house so i will put the disconnects there and the existing pane will stay where it is and the 100amp panel will be installed in the upstairs apartment..
Will i need a 2 meter 200 amp meterbase & 200 amp disconnects or can i wire a 100 amp disconnect off one side of the meter with 100amp service cable... is that allowed by code?
 

·
Registered
Joined
·
5 Posts
Discussion Starter · #4 ·
I've done electrical work in the past and can change service.... the electic company says the meter has to be moved to the other side of the house so i will put the disconnects there and the existing pane will stay where it is and the 100amp panel will be installed in the upstairs apartment..
Will i need a 2 meter 200 amp meterbase & 200 amp disconnects or can i wire a 100 amp disconnect off one side of the meter with 100amp service cable... is that allowed by code?
 

·
Licensed Electrician
Joined
·
4,352 Posts
Depending on the existing wiring, this may not be even possible without a major rewire of the house. I would bet that, if the house has always had one service, that the circuits are intermixed between the first floor and second floor.

I would check with the local electrical inspector as he MAY require a third panel for the "public" areas.
 

·
Registered
Joined
·
5 Posts
Discussion Starter · #6 ·
Ill be living in the bigger apartment so a common area panel isn't an issue... and i already started seperating the circuits, it was easy since each apartment was wired seperately even though they all went to the same panel... I'm adding junction boxes were needed and have attic access to run new homeruns to the upstairs unit..
 

·
Licensed Electrician
Joined
·
4,352 Posts
Keep in mind that when you are running new home runs, the circuits you connect them to will need to follow the current code cycle for your area.

For example: If you need to refeed a kitchen circuit, it will need to be a 20 A circuit, and the outlet you are refeeding will need to be a GFI. If you are refeeding a general lighting/outlet circuit, it will need to be put on a AFCI breaker.
 

·
Registered
Joined
·
5 Posts
Discussion Starter · #8 ·
It's actually wired correctly... the only new additional work is, remove all electric baseboard heaters and wires, add 2 central hvac units, wire the garage and 2 seperate laundry rooms.
 

·
Licensed Electrician
Joined
·
4,352 Posts
I was just going off this statement...

I'm adding junction boxes were needed and have attic access to run new homeruns to the upstairs unit..
But it seems as if you got it under control.
 

·
Licensed Electrician
Joined
·
4,352 Posts
I just bought a 2 unit home..but....found there is only one 200 amp meter and electrical panel... I want to keep the main unit (1000sq.ft)downstairs on the 200 amp panel (where I will live), and the second unit upstairs a 100 amp panel since its smaller 700sq.ft.
Do i need a 200 amp double meter? What size service feeder? and disconnects???? HELP!!
Typically, we would install a 150 A service with 2 100 Amp panels.

You might be able to install a 2/G (duplex) meter/main combo with 100 A mains and reuse the 200 A panel, but I would check with the electrical inspector before assuming anything.

If you install 100 A mains, you would need to run #3 CU or #2 4-wire SER cable between the mains and sub panels. The line side of the meters would decide on what size the service coming to the house is rated at. I have learned thru these forums, there are a multitude of different local and POCO requirements to tell you for sure what are normal sizes for your area. This is why I recommend discussing the service change with the AHJ.

Shoot, we don't even know if you can legally do the work in your area.
 