It will give you more protection since each ground rod is on a different ground plane.I believe the 2 ground rods were decided as an alternate to the one.with just one rod,code requires a rather expensive test to determine if it will fall below a certain #. I think 2 rods will not give you any more protection then the one you already have.
In theory.It will give you more protection since each ground rod is on a different ground plane.
The NEC does not require test. The inspector can request a megger test. Since he has to witness the test and can take several days to get to the job for the test. It is easier to drive the second rod and forget about it. Otherwise the EC can sit and wait for the EI to witness the test. If the test proves less than 25 ohms, no second rod is required.I believe the 2 ground rods were decided as an alternate to the one.with just one rod,code requires a rather expensive test to determine if it will fall below a certain #. I think 2 rods will not give you any more protection then the one you already have.
Well if there's no test then how does one know that 2 rods will do the job and not just one rod?The NEC does not require test. The inspector can request a megger test. Since he has to witness the test and can take several days to get to the job for the test. It is easier to drive the second rod and forget about it. Otherwise the EC can sit and wait for the EI to witness the test. If the test proves less than 25 ohms, no second rod is required.
We don't. The NEC does not require more then two rods. I don't require the second rod. But if there is only one rod, I request the megger test. I have three days to complete the inspection including witness the test. It is cheaper to just drive two rods and be done with it.Well if there's no test then how does one know that 2 rods will do the job and not just one rod?
Hey Allen you may have to start a new thread on that to get a answerI should ask, if the building has an entering water pipe or a concrete reinforcing bar as a grounding electrode, is just one ground rod sufficient?
No. If you use rodI should ask, if the building has an entering water pipe or a concrete reinforcing bar as a grounding electrode, is just one ground rod sufficient?
I have only one myself. It was inspected when I did the service upgrade about 15 years ago. I have no intentions to install another one, nor am I required to.