I've read other discussions on this, but I'm still not completely sure if this meets code.

I'm in the process of remodeling a 1920's home which will have:

  • A Main Floor Bathroom with
    • (1) GFCI receptacle (on a 20A dedicated circuit)
    • (1) Exhaust fan/light over the shower (on the same 20A dedicated circuit)
    • (2) vanity lights (utilizing an existing 15A circuit)
    • (1) ceiling light (also utilizing the existing 15A circuit)
I would like to use the same two circuits described above for the:

  • 2nd Floor Bathroom that has
    • (1) GFCI receptacle (on the same 20A dedicated circuit)
    • (1) Exhaust fan/light within 18 inches the shower (on the same 20A dedicated circuit)
    • (2) vanity lights (also utilizing the existing 15A circuit)
Does this meet code? Or do I need to dedicate a 20A circuit to each bathroom?

Thanks! :)
 

·
" Euro " electrician
Joined
·
5,369 Posts
I've read other discussions on this, but I'm still not completely sure if this meets code.

I'm in the process of remodeling a 1920's home which will have:

  • A Main Floor Bathroom with
    • (1) GFCI receptacle (on a 20A dedicated circuit)
    • (1) Exhaust fan/light over the shower (on the same 20A dedicated circuit)
    • (2) vanity lights (utilizing an existing 15A circuit)
    • (1) ceiling light (also utilizing the existing 15A circuit)
I would like to use the same two circuits described above for the:

  • 2nd Floor Bathroom that has
    • (1) GFCI receptacle (on the same 20A dedicated circuit)
    • (1) Exhaust fan/light within 18 inches the shower (on the same 20A dedicated circuit)
    • (2) vanity lights (also utilizing the existing 15A circuit)
Does this meet code? Or do I need to dedicate a 20A circuit to each bathroom?

Thanks! :)
Kinda meet the code but it will not really fly in most places AFAIK.

To meet the code 100% this what you will have to do two options one is have both bathroom receptales on one circuit however nothing else will be hook up to it and the light from other circuit which you can use just remember you will have to use the AFCI for this due most states will required it if you are on 2005 or later NEC codes,

Or second option which I rather do this often

Run it own circuit for each bathrooms that useally take care of it.

Merci,
Marc
 
  • Like
Reactions: andy0107

·
Licensed electrician
Joined
·
13,379 Posts
Marc gave you the code breakdown. I prefer the receptacles to be dedicated to a bathroom, but not shared as the code allows. This gives you more flexibility if multiple people want to dry their hair at the same time.
 

·
Super Moderator
Joined
·
20,886 Posts
It does not meet code. If you are going to share the 20 circuit between bathrooms you can only have receptacles on it. You must remove the fan/lights from the circuit.

The other option is a 20 amp circuit to each bathroom. Then you can put everything on the 20 amp circuits as long as it is within the one bathroom. You can still leave the 15 amp for lights if you wish or you can move the lights to the 20 amp and use the 15 amp somewhere else.
 

·
Licensed electrician
Joined
·
13,379 Posts
I would like to expand on Joed's comment. The fans and lighting installed in place must be less than 50% of the circuit capacity.
 
  • Like
Reactions: andy0107

·
Tearing it apart.
Joined
·
2 Posts
Discussion Starter #6
Thanks All!

Great advice and thanks for clearing the code issues up for me.

I've decided to use 2 separate 20A circuits - one for each bathroom. Each circuit will have the GFCI receptacle and exhaust fan/light on it.

I will power the vanity lights and ceiling light in both bathrooms from a single existing 15A circuit.

Thanks again!:thumbup: