I have a total of eight incandescent clear service bulbs lighting the interior of a pole barn. Five of the sockets have 300 watt bulbs and three have 150 watt bulbs. No light switch - these are all wired to one 15 amp circuit, with the breaker used to turn them all on/off. All wiring is 12/2. My questions, and thanks in advance for your patience if this has been answered elsewhere:
- 1950w/120v = 16.25 amps, so this is obviously overloaded. Can I simply replace the 15 a breaker with a 20 a and consider it fixed?
- Two of the sockets using 150 watt bulbs are newer (all else is 30 years old), and are standard ceramic bulb sockets. Is it OK to use these higher-wattage bulbs in the standard ceramic sockets you can buy anywhere?
- Is it a bad deal to be using the breaker for a main switch? If so, and I should look at installing an actual switch inline, can I use something standard?
Thank you for any/all help and input!