Is it OK to use 14 gauge wire on a 20 amp small appliances circuit? (or a last part of the circuit at that branch off and terminate)

Considering the multiple recepticles are 15 AMP, I don't think there is a need to use 12 gauge?
 

· Remodeler
Joined
·
215 Posts
Yep, 20A breaker needs 12 gauge wire as per code.

But here is a theoretical question that makes sense in my mind. Let's say you have a few outlets on a 20A breaker and all are wired with 12 gauge wire. Assume you want to add a doorbell, and you tap power off of the last outlet in that 20A circuit. So you have to run wire from that last outlet to the 12 or 16 volt doorbell transformer. So beyond the outlet, the only possible draw of power will be the dinky little doorbell. So why wouldn't a gauge smaller than 12 be allowed between that last outlet and the doorbell transformer since it doesn't seem possible that anything beyond that last outlet will be drawing a lot of amps? I would think it would be okay to just use 14 guage between the outlet and the doorbell transformer. But I assume the answer is no. Just curious if anyone has any insight. Thanks.
 

· Registered
Joined
·
335 Posts
Discussion Starter · #6 ·
Yep, 20A breaker needs 12 gauge wire as per code.

But here is a theoretical question that makes sense in my mind. Let's say you have a few outlets on a 20A breaker and all are wired with 12 gauge wire. Assume you want to add a doorbell, and you tap power off of the last outlet in that 20A circuit. So you have to run wire from that last outlet to the 12 or 16 volt doorbell transformer. So beyond the outlet, the only possible draw of power will be the dinky little doorbell. So why wouldn't a gauge smaller than 12 be allowed between that last outlet and the doorbell transformer since it doesn't seem possible that anything beyond that last outlet will be drawing a lot of amps? I would think it would be okay to just use 14 guage between the outlet and the doorbell transformer. But I assume the answer is no. Just curious if anyone has any insight. Thanks.
You can do all kinds of things that makes sense but I would think, code is code.
That's not to exclude the possibility that in 20 years you are changing out that door bell for a laser sentry gun that draws 16 amps. :)
 

· Banned
Joined
·
17,249 Posts
You can do all kinds of things that makes sense but I would think, code is code.
That's not to exclude the possibility that in 20 years you are changing out that door bell for a laser sentry gun that draws 16 amps. :)
And what would prevent someone from seeing that 14g in the future & connecting a heavier load? Then someone else realizes the 20a breaker shuts off power to that device & puts in an even heavier load
Code is there for a reason...12g wire....20a breaker
14g wire =15a breaker

You can't always prevent someone from doing something wrong
But code tries to prevent problems
My last house was 100 years old - many owners
This house is going on 60 years old - quite few owners too
Some houses change ownership every 5 years or less
 

· Civil Engineer
Joined
·
5,832 Posts
The entire theory of wire gauge size and breakers is based on protecting the WIRE from overcurrent conditions. The devices have their own protection. So the theory is that a circuit protected with a 20A breaker could have up to 20 amps on the wire before the breaker blows. Therefore, a fault on any downstream device (i.e. the doorbell) could cause up to 20A of current on the 14 gauge wire.

In theory, the insulation on the 14 gauge wire could overheat given the overcurrent (20A) condition, potentially causing a fire. While this is unlikely, it is the reason why code prohibits less than 12 gauge wire on a 20A circuit.
 

· DIY'r
Joined
·
523 Posts
Or what if you picked up a dead short at the transformer or someplace in the #14 wire? Nice fried wires.
To be fair, a dead short would overheat any wire if power were not cut by the OCPD.

The breaker would trip before the #14 would fry (hopefully).

Daniel Holzman said:
The devices have their own protection.
Which devices? Most do not.. The OCPD should be sized for the lowest rated component of the circuit. If you used all #12 wire, but connected a receptacle inline with the branch wiring that was rated for max. 15A pass-through, the circuit would have to be protected by a 15A OCPD.
 

· Remodeler
Joined
·
215 Posts
But most recepticles I buy now is 20A passthrough, right?
Any 20A outlet you buy now should look like this:



Notice has the neutral slot has the additional little slot coming off of it at 90 degrees. A 15A outlet won't have that perpendicular slot coming off the neutral slot. But the fail proof method to see the amperage of the outlet is to read the back and/or side; it will always say.
 

· Licensed Pro
Joined
·
1,571 Posts
But most recepticles I buy now is 20A passthrough, right?
Yes, they are.

And just to be clear, while it is a violation to use 14ga wire on a 20A circuit in most cases, the 14ga wire will not burst into flames or all the insulation melt off if the current goes to 20A.
 

· Banned
Joined
·
17,249 Posts
Any 20A outlet you buy now should look like this:



Notice has the neutral slot has the additional little slot coming off of it at 90 degrees. A 15A outlet won't have that perpendicular slot coming off the neutral slot. But the fail proof method to see the amperage of the outlet is to read the back and/or side; it will always say.
There is no need to buy a 20a outlet unless you have a 20a plug
The 15a outlets are rated as 20a pass-thru
A good place for a 20a outlet woudl be in the garage/shop
I've yet to own any tool that has a 20a plug on the end
 

· Registered
Joined
·
335 Posts
Discussion Starter · #16 · (Edited)
Thanks everyone
did it all with the yellow 12 GA,

The jacket is as thin as the old 14 GA anyway.

Yes I used 15AMP receptacle for this add on.


I have gotten 20 AMP receptacle on my microwave and dishwasher circuits.
microwave being the only thing on the circuit, calls for a 20 AMP receptacle even the plug is 15AMP style
plus, it have great plug retention
 

· Banned
Joined
·
5,990 Posts
Yes, they are.

And just to be clear, while it is a violation to use 14ga wire on a 20A circuit in most cases, the 14ga wire will not burst into flames or all the insulation melt off if the current goes to 20A.
No, but the temp. rise above ambient will be (20/15)^2 times what it would be if the wire carried 15A.
I guess the insulation will just get brittle faster.
 

· Licensed Pro
Joined
·
1,571 Posts
No, but the temp. rise above ambient will be (20/15)^2 times what it would be if the wire carried 15A.
I guess the insulation will just get brittle faster.
Not really. Remember, the listed ampacity for 14ga THHN (which is really what NM-B is) is 25A. It's the NEC that mandates, for most applications, the OCPD be limited to 15A.
 

· Banned
Joined
·
5,990 Posts