I was looking in my circuit breaker box and I noticed that some 14-2 cable used for several overhead lights is connected to a 20 amp switch instead of a 15 amp. It has been this way for a while. Is this something I should fix immediately or can it wait till I have to go into the switch box for something else?
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
Fix it right away, regardless of how long it has been like that.
 

·
Super Moderator
Joined
·
22,148 Posts
20 amp switch is not a problem. 20 amp breaker is a problem. Change breaker to 15 amp if you mean beaker instead of switch.
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts

·
Registered
Joined
·
1,667 Posts
Worst case; If it's old wiring, it could overheat and cause a fire.
If it's the newer, 90C wire, then nothing much except that you will get a larger voltage drop on the run, which could cause some appliances to overheat or not perform as well as they should.

Definitely change the breaker to 15A, unless you want to change ALL of the wire on the circuit to #12.

FW
 

·
Registered
Joined
·
780 Posts
Most likely nothing would happen. It is an NEC code violation but the NEC has a significant safety margin built in. If it's just lighting circuits it's doubtful you would be drawing much more than a couple of amps anyway.
 

·
Registered
Joined
·
29 Posts
Most likely nothing would happen. It is an NEC code violation but the NEC has a significant safety margin built in. If it's just lighting circuits it's doubtful you would be drawing much more than a couple of amps anyway.
and 14 is technically rated for 20 amps too, but yeah there's that pesky code issue hehe, and the voltage drop over distance.
 

·
Registered
Joined
·
780 Posts
and 14 is technically rated for 20 amps too, but yeah there's that pesky code issue hehe, and the voltage drop over distance.
Yes a code issue, but not likely an emergency situation and changing to a 15 amp breaker is going to do little to solve a voltage drop situation.
 

·
Registered
Joined
·
1,667 Posts
Yes a code issue, but not likely an emergency situation and changing to a 15 amp breaker is going to do little to solve a voltage drop situation.
No, changing to 15A breaker will not change the voltage drop issue, but I was thinking of the situation if more than 15A were being drawn on the branch.

FW
 

·
Registered
Joined
·
780 Posts
No, changing to 15A breaker will not change the voltage drop issue, but I was thinking of the situation if more than 15A were being drawn on the branch.

FW
The NEC codification requirements has a significant safety margin built in, even drawing 20 amps on a 14 ga branch is not likely to create enough heat to cause a problem. The breaker should be changed to bring it into code but it is not an emergency situation.
 