No it won't. The only way to know for sure is to take voltage readings.

One dead giveaway though is if one of the phases has no single pole breakers on it. Then it's most likely a delta.

Another way is to measure voltage on a known device that uses two phases. If it's close to 208, it's a wye. If it's more like 240, it's a delta.
 

· Registered
Joined
·
10,393 Posts
Not unless someone put the label on it.

Measure the voltage between hot and neutral, or between two hots, as needed if you are encountering this panel for the first time.

A 120/208 volt 3 phase system will have 120 volts from any hot leg to neutral (and 208 volts between any two hots).

A wye 3 phase system has hot to neutral voltage the same for all three phases.
 

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts
If it's 120/208, then it's a wye system by definition. If there's no neutral present then it can only be used for delta-connected loads - but it's still a wye system. The square root of three (1.73) ratio of voltages indicates that the grounded conductor is at the "midpoint" of the three hot legs on a phase diagram, which is achieved by connecting the transformer secondaries in a wye configuration.
 

· Registered
Joined
·
756 Posts
If it's 120/208, then it's a wye system by definition. If there's no neutral present then it can only be used for delta-connected loads - but it's still a wye system. The square root of three (1.73) ratio of voltages indicates that the grounded conductor is at the "midpoint" of the three hot legs on a phase diagram, which is achieved by connecting the transformer secondaries in a wye configuration.
Not always.

Mark
 

· Registered
Joined
·
10,393 Posts
There is no raison d'etre for (and no socially redeeming value of, and no easy way of producing) a 120/208 volt system that is not from a symmetric wye configuration.

The reason 208 volts became accepted as a standard is because it is the natural result of configuring a return conductor to have 120 volts potential from each of the 3 legs of a 3 phase system. It combines the advantages of 3 phases with the advantages of 240 volts over 120 volts (fewer or thinner conductors needed), although some appliances come in slightly different versions for 208 versus 240 volts.

Also the high leg, or stinger, is the natural result of configuring a return conductor having 120 volts potential from each of two legs of a 240 volt 3 phase system so as to provide a 120/240 volt feed (or subfeed).
 
  • Like
Reactions: mpoulton

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts
Not always.

Mark
What's an example of "not always"? To produce a 208V delta without wye-connected secondaries would require transformers with 208V secondaries - and that's very odd. To produce a 208V delta with 120V from each hot to ground and not use a wye configuration would be... darn near impossible. I can't think of an easy way to do it.
 