DIY Home Improvement Forum banner

12/3 to garage

851 Views 7 Replies 4 Participants Last post by  mudslinger
Hello, its been a long while since ive visited.
I have a 12/3 w ground existing underground from my house to the garage. The run from the main box to the garage is 80'. I'd like to ask what the best configuration in terms of the most power to the garage, using the existing wire. As it stands I've set it up as 1 20a circuit with the 3rd wire unused. I'm hoping for 2 20a circuits, but am unsure with the single common.
Thanks in advance
1 - 4 of 8 Posts
Ok. Double pole 20 at the main. Now at the garage sub, I would use 2 20a breakers with a bonded ground and ground rod?
Thanks
I over do most things, and wouldnt mind breakers in the garage to save going back to the house in case of overload, I,m dabbling in woodworking and theres a fairly heavy initial draw from the air compressor and saws. Would the breakers and ground rod be a problem? Nothing has tripped the main up to this point, but the lights draw down.

thanks
1 - 4 of 8 Posts
This is an older thread, you may not receive a response, and could be reviving an old thread. Please consider creating a new thread.
Top