Discussion Starter #1
Hello,

Need to run (2) lines of 12-2 with ground underground feeder for irrigation pumps. One line will be 240v and one will be 120v.

Need to go under a walkway. Can I place both of these lines in 3/4" conduit under the walkway only? 1" conduit? If neither, what size conduit do I need while going under the walkway?

Thanks in advance for your assistance.
 

·
Super Moderator
Joined
·
8,874 Posts
Are you using the conduit just for the walkway, or the whole distance?

Under the walkway, is fine.
 

·
Registered
Joined
·
113 Posts
Discussion Starter #3
Are you using the conduit just for the walkway, or the whole distance?

Under the walkway, is fine.
Thanks for the reply.

It will just be in conduit under the walkway. Wanted to make sure there wasn't any issue with placing it in the 1" conduit (overheat, etc)?

Thanks again for taking the time to reply.
 