The obvious question is are SURE nothing else is running on that circuit?
Does the blender turn at all? Tried a different outlet? Try it without the container and empty.My new Vitamix blender is rated at 11.5 amps, but twice tripped the circuit breaker when I used it for the first time a few days ago. The circuit breaker has the number "20" on the switch; I assume it's a 20 amp breaker.
I plan to talk to Vitamix about this, but would like some feedback from the likelier-to-be impartial forum visitors here: do you think I received a blender with a bad motor? Or are there circumstances in which even a 20 amp circuit might not be enough for a heavy duty blender?
My new Vitamix blender is rated at 11.5 amps, but twice tripped the circuit breaker when I used it for the first time a few days ago. The circuit breaker has the number "20" on the switch; I assume it's a 20 amp breaker.
I plan to talk to Vitamix about this, but would like some feedback from the likelier-to-be impartial forum visitors here: do you think I received a blender with a bad motor? Or are there circumstances in which even a 20 amp circuit might not be enough for a heavy duty blender?
Which is every pretty much breaker made in the last 30+ years.You need the correct type of breaker,
One with a slow trip,
these types of breakers are designed to cope with the high start up
currents of a motor.
We call them slow-blow,
I think you guys call them type 2 ?
Most of the Americiane breakers are class B or C ( more like halfway between the two ) so it pretty common beside the AFCI they are it own legand ( some are good and some are merde. ) But the GFCI's is about pretty close to our RCD's even your verison of RCD'sIs the rating 11.5 amps the running current ?
If so the starting current could be much higher !
You need the correct type of breaker,
One with a slow trip,
these types of breakers are designed to cope with the high start up
currents of a motor.
We call them slow-blow,
I think you guys call them type 2 ?
11 amps for the fridge ?? is that a big unit like Wolf or Sub-Zero unit ?Maybe you'll think I'm an odd one, but I'm going to run the Vitamix from a long extension from the garage wall plugs until I hire an electrician to do something with my circuit panel. (I don't trust myself to do the job on my own.) The 20 amp kitchen circuit is on a regular, non-AFCI breaker, but it already has an 11 amp fridge running on it.
I opened the thread because I had thought something was wrong with the Vitamix's motor. I really like the machine otherwise, so if it's working the way it should I'll hold onto it.
Firstly, the fridge should to be on its own 15 amp circuit (in canada that is, its probably the same in the US...in theory the motor could draw as much as 6 times the FLA at start up (full load amperage) of the blender, but i doubt that they would sell an appliance that would draw that much (ever notice that when you turn on your vacuum the lights dim momentarily)...also, a 20amp kitchen branch circuit can only have 2 outlets on it (once again canadian standards)...MidgeTenant said:Maybe you'll think I'm an odd one, but I'm going to run the Vitamix from a long extension from the garage wall plugs until I hire an electrician to do something with my circuit panel. (I don't trust myself to do the job on my own.) The 20 amp kitchen circuit is on a regular, non-AFCI breaker, but it already has an 11 amp fridge running on it.
I opened the thread because I had thought something was wrong with the Vitamix's motor. I really like the machine otherwise, so if it's working the way it should I'll hold onto it.