Trap In Horizontal Gas Lne - Plumbing - DIY Home Improvement | DIYChatroom
Old 01-11-2016, 01:48 PM   #1
trap in horizontal gas lne
I'm retrofitting an on-demand propane hot water heater in a situation where the gas line comes in at a height such that it's a horizontal run to the regulator and then a short 90 degree turn to the heater connection. Regulator has to be installed horizontally for lock-up to function properly. I need a trap upstream of the regulator, and I'm wondering about how to properly install a trap in a horizontal line, if that is even possible. Do I need to put a short vertical jog in the line just to install the trap and then on to the regulator? Seems like a horizontal tee wouldn't be that effective, but maybe ok if within (how much?) xxx of the regulator?
Thanks for any insights.
GaryAitken is offline   Reply With Quote
Old 01-12-2016, 03:47 PM   #2
An old Tradesmen
Rewards Points: 9,466
Moved to plumbing forum.
Old 01-12-2016, 04:30 PM   #3
Rewards Points: 6,440
The pic that includes text is correct. The line from the gas valve to the T is - " Bull Headed " - into the T. The drip leg is piped into the T " running ".
The incorrect method shows the drip leg " Bull Headed " into the T. The line from the gas valve into the T is " running ".
My regulator is at the tank so I can't give you any more specifics on distance.
Old 01-12-2016, 08:07 PM   #4
clarification and question
Thanks SeniorCitizen (that makes two of us...),
Just for clarification -- the photograph, showing the tee running horizontally, drip leg vertical, is incorrect. The drawing, showing the tee vertical, is correct. Yes?
I have a situation somewhat like the photograph, where the gas line, which is rigid, approaches the regulator horizontally. How much of a vertical above the drip leg is required? Would it be sufficient to run the gas line into the bullhead with the tee vertical, and come off the top of the tee with a 90 deg. bend and into the regulator?
Old 01-12-2016, 08:46 PM   #5
Although not ideal, your proposal would be better than the set up in the photograph because your install would cause the gas flow to change directions at the T and that's a positive.
Tags
demand water heater , gas line trap
HELP - Broken Sink Trap Fitting NIGHTMARE! Steve Sr Plumbing 17 03-10-2013 05:45 PM
PVC trap adapter on galvanized trap? dougan Plumbing 2 10-05-2012 06:16 AM
Would this be a 'P' trap or an illegal 'S' trap? klondiker Plumbing 7 04-06-2012 10:18 PM
Trane XR90 - Condensate Drane Trap JDWorks HVAC 16 02-07-2012 07:59 PM
kitchen wall drain outlet higher than trap arm Druidia Plumbing 24 10-13-2011 12:39 PM