I am looking into replacing an electric stovetop with gas, so I looked into the sizing requirements to see if the existing lines were large enough to tap into. In the attached pic, the sizing calcs suggest it would be possible to add a 1/2" lateral onto the existing system without having to dismantle too much of what is already in place. Thoughts?
tns1 is offline   Reply With Quote
Old 07-10-2015, 03:06 PM   #2
Rewards Points: 6,652
You need 3/4" from the 1.25" Main to the stove. 1/2" will not cut it.
Old 07-10-2015, 03:33 PM   #3
Plumber
TheEplumber's Avatar
Rewards Points: 240
You're undersized at the new tee location. The branch serving the new range and WH will need to be increased. That means replacing the 1 x 1/2 x 1/2 tee
1/2" to the range appears OK
The Following User Says Thank You to TheEplumber For This Useful Post:
ben's plumbing (07-12-2015)
Old 07-10-2015, 04:14 PM   #4
Rewards Points: 322
I see. The short 1/2" pipe section between the existing tee and this new tee I proposed would be undersized for the additional flow. I was hoping I would not have to remove that existing tee. Those laterals in the drawing are not simple straight sections, but snake down into the framing. Dis-assembly is not the issue, but rebuilding the laterals with rigid pipe would require punching holes in the walls.
Any techniques that might help me out here? For instance are unions allowed? Could I use the bendable gas pipe to replace some of the convoluted sections?
Old 07-10-2015, 07:40 PM   #5
You could run CSST. But you will have to make some holes. Personally I would cut a section in the wall, then get a box to put in there to allow you to place the line in the recessed opening. Then just bring the proper line up for the stove.
Because you only have 1/2", and most stoves have a high BTU gas burner now. You really need to run 3/4".
Old 07-11-2015, 01:26 PM   #6
Rewards Points: 1,910
He has a 50,000 btu stove. The 1/2 is enough for the run to the stove. The only issue is the section supplying both the stove and the WH as Eplumber said.
Old 07-11-2015, 02:39 PM   #7
Not with the high output BTU burner. If they turn on other burners at the same time. It waill actually cause
issues. That is why they need to run the 3/4".
Old 07-11-2015, 09:42 PM   #8
A 50,000 btu stove is 50,000 btu with all burners on high. It won't ever be more than that. 1/2" will handle 50,000 btu.
Old 07-11-2015, 10:41 PM   #9
Actually not. We have a stove with a high BTU burner. When you turn on the other four, it actually causes them to go down in flame height, because of the other burner.
3/4" comes off of the 1" for my Water Heater & Stove. I have a run of 1" that is just for the furnace. It was done that way originally, because when we moved into the house, there was still an Octopus Furnace down there.
There really is not much cost difference between 1/2 & 3/4. Personally I would have the OP go with the 3/4", so that later on down the road, they do not come back wondering why the appliance is fuel starved.
Old 07-12-2015, 07:10 AM   #10
An old Tradesmen
Rewards Points: 9,408
If the OPs stove is fuel starved when using the largest burner with any other burners, then there is a problem with the gas supply to the house. 20' of 1/2" black pipe will flow 75,000 BTUs an hour. The OP listed his stove as a 50,000 BTU. He has 20% safety with a 1/2" line and the few fittings he will need.
As pointed out earlier, the tee needs to be increased in size for the water heater and stove line.
Old 07-12-2015, 07:51 AM   #11
Property Mgt/Maint
Rewards Points: 8,202
since you need to break into the main line, it may be easier to the leave the T-for the water heater intact and find another location on the main line to T off for he new stove, just a thought
[political signature removed]
Yodaman is offline   Reply With Quote
Old 07-12-2015, 07:57 AM   #12
Rewards Points: 582
if it were mine I would change it ti this....
Old 07-12-2015, 10:05 AM   #13
Property Mgt/Maint
Ben, could not agree more if doable with out remodeling the house. Fewer lineal feet, fewer connections, = few possibilities for leaks!
Old 07-12-2015, 10:33 AM   #14
It looks like OP is using multiple code zones to size his lines (70, 80, 90 and 100 feet). At least that's what the notes under the measurements appear to be to me as someone who uses a different code. Without knowing the actual lengths from point of delivery, as well as the actual delivery pressure, only assumptions can be made.
hvac benny is offline   Reply With Quote
Old 04-12-2017, 11:46 PM   #15
Rewards Points: 322
Re: Natural gas piping question
I realize I hadn't finalized this old thread. I ended up changing out the 1" x 1/2" x 1/2" tee to 1" x 3/4" x 1/2", and ran 3/4" all the way to the new stove. A bit tricky disassembling and reassembling those laterals in the walls and attic, but it all worked out. No fireballs.
Is Natural Gas Firepit on a Wood or Composite Deck unsafe? Jakobud General DIY Discussions 4 03-29-2012 03:43 PM
Generator connection Question - Final Plan Apollo67 Electrical 24 01-30-2012 07:44 PM
DIY LP piping question cgschlangen Plumbing 4 11-03-2011 10:22 PM
natural gas install to existing house sagechickie Building & Construction 9 04-22-2009 09:44 PM
Basement Renovation Question KUIPORNG Remodeling 234 08-26-2008 08:19 AM