Laundry Standpipe Weir And Change In Elevation Of Vented Branch - Plumbing - DIY Home Improvement | DIYChatroom
Old 07-02-2015, 12:55 PM   #1
Rewards Points: 91
Laundry standpipe weir and change in elevation of vented branch
I know there are rules that specify that the trap weir can't be higher than the top of the pipe at the vent opening, as also shown in the next picture:
but wasn't sure if I can add a vent BEFORE the 45s, and then it would be OK to make the change in elevation.
Would the following (below image) be permitted?
I am in NY state.
toddmanqa is offline   Reply With Quote
Old 07-02-2015, 01:30 PM   #2
Rewards Points: 1,938
Is there some weird reason you need to cock the trap drain like that? If you revent it like shown it may be legal unless the vent wye is to close to the trap.
Old 07-06-2015, 04:16 PM   #3
Special User
Rewards Points: 1,230
As far as I know, yes, what you propose is legal under the UPC but as Ghostmaker points out the trap arm (between the trap weir and the vent opening) must be at least two pipe diameters long. So for 2" pipe, you need at least 4".
Also, your re-vent needs to either 1) rise 6" above the top of the standpipe before turning to go horizontal and join the VTR (Vent Through the Roof), or 2) rise at least 6" above the top of the trap arm and use swept drain fittings, not hard-90 vent fittings.
The above post is for entertainment purposes only. Its contents may, and probably will, lead to legal liability and damage or loss of property, life, or limb. Use at your own risk.
tylernt is offline   Reply With Quote