Would 277v Lighting Circuit Be Considered MWBC - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 03-16-2010, 08:03 PM   #16
Rewards Points: 506
Originally Posted by Stubbie View Post
You must have a neutral not a grounded leg to have an MWBC.
Huh? Could you explain further?
jlmran is offline   Reply With Quote
Old 03-16-2010, 08:46 PM   #17
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
See post #2
Multiwire branch circuits have a shared neutral that serves two hot wires not one. A grounded leg of a 120 volt or 277 volt single phase 2 wire branch circuit carries all the current of the single hot wire and is therefore not a neutral. A mwbc shares a grounded leg that serves to carry the unbalanced current (difference between) two hot legs of opposite ends of the transformer. This makes the grounded leg a neutral wire ...neutrals carry the diffence in current of two or more ungrounded conductors.
Just becasue a branch circuit has multiple wires does not make it an MWBC...
You need this to have a mwbc voltage has nothing to do with it.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 03-16-2010, 08:53 PM   #18
Rewards Points: 506
Very nice, Stubbie. Thanks.
Old 10-22-2010, 02:36 PM   #19
Seasoned DIYer
Rewards Points: 150
Originally Posted by kbsparky View Post
277 Volts from a MWBC would involve using a 480 Volt source. Not exactly a DIY project.
Not all that worse than European projects, where originally 240v countries get its power from 415Y/240 sources.
There was a lawsuit somewhere in which someone was hurt when something happened to him involving a leg and a ground on 277v lighting wiring in the state of California. The worker wasn't trained for working over 300v and lawyer argued that 277v is part of 480v, thus exceeding his <300v training, but the judge threw that out.
http://ecmweb.com/mag/electric_dangers_working_hot/
HVAC_NW is offline   Reply With Quote
Old 10-22-2010, 03:07 PM   #20
Rewards Points: 330
oleguy74 is offline   Reply With Quote
Old 10-22-2010, 03:10 PM   #21
Rewards Points: 330
A two wire with ground 277 volt branch circuit is no more a MWBC than a two wire with ground 120 volt circuit. You must have a neutral not a grounded leg to have an MWBC.
the neutral is the grounded leg.the ground wire is the grounding wire.per code.
Old 10-22-2010, 08:19 PM   #22
Rewards Points: 2,800
One hot wire and one neutral wire (for example standard U.S. 120 volt circuit) -- Not a MWBC.
Two hot wires and no neutral wire (for example a 240 only volt heating circuit in the U.S.) -- Not a MWBC.
In a 277/480 volt symmetric (wye) 3 phase circuit/service, if you are supplying the lights using two or all three of the hot lines along with the neutral, then you ahve a MWBC. If you use just one of the hot wires and the neutral, you do not have a MWBC supplying the lights.
Stick to your lawn watering schedule until it really starts to pour. After the storm you have only the same number of rest days you always had and then you need to start watering again.
Old 10-28-2010, 03:50 AM   #23
Seasoned DIYer
Rewards Points: 150
I couldn't remember the name of it, but what about a duplex on opposing poles with shared linkage on neutral side and jumper removed on hot side so that top and bottom are on opposing poles?
Old 10-28-2010, 05:39 AM   #24
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 2,006
There is no name for that. It is simply a MWBC to a device where two circuits are sharing the same yoke.
Wiring in New Addition? sandyman720 Electrical 6 11-27-2011 03:34 PM
Loose electrical outlets travishume Electrical 30 08-01-2008 07:21 PM
Conflicting Circuit Info!?? BenBil Electrical 9 01-15-2007 08:26 AM
So lost - electrical requirements please help lapsis9 HVAC 4 12-20-2006 08:09 PM
Adding new circuit breakers to 100 amp sub panel DrP Electrical 8 05-25-2006 10:05 PM