I have parked my trailer behind and barn on a cement pad and I would like to run a wire from the panel approximately 160 ft (10/2) with a 20 amp breaker. I have a 30 amp plug on the trailer and the 20 amp should be sufficient for what I want.
When running the wire/cable from the outside of the barn I will have it protected by a PCV pipe to the ground at which I will put it under ground directly beside the cement pipe. The cable is water proof but will also have this cable running under ground inside another pipe to protect it. The wire/cable will come upon the other side of the cement pad to a post where it will be protected again by PVC pipe running to a receptacle there to plug in my trailer. The Receptacle box will be sealed with a weather proof lid. I know that without a GFI I have the dig the the trench for the wire 18 inches. However with the pipe protecting the wire will I only have to dig 12 inches or less?
Thankx
eechoo is offline   Reply With Quote
Old 04-07-2010, 08:12 PM   #2
Super Moderator
joed's Avatar
Rewards Points: 29,286
With a 30 amp plug you will need a 30 amp receptacle. You can't put a 30 amp receptacle on a 20 amp circuit. Put in a 30 amp breaker.
Old 04-07-2010, 08:20 PM   #3
Master Electrician
not to mention the fact that a 20A twistlock and a 30A twistlock aren't compatable. I'm not overly familiar with NEC rules but i think with or without pipe and no gfci you still have to go to the maximum depth.
andrew79 is offline   Reply With Quote
Old 04-07-2010, 10:49 PM   #4
Electrical Contractor
jbfan's Avatar
Rewards Points: 6,054
30 amp, 120 volt circuits do not need to be gfci protected(05 code)
Yes I am a pirate, two hundred years too late
The cannons don't thunder, there's nothing to plunder
I'm an over-forty victim of fate.
jbfan is online now   Reply With Quote
Old 04-08-2010, 03:17 AM   #5
Rewards Points: 1,016
Does your trailer have a TT-30P connector - which mates to a TT-30R recepticle? I would think probably so.
Here is a link that provides information (click on the 30a service selection on the left of the page): http://www.myrv.us/electric/
If you have an adapter to convert the TT-30P to a regular household type plug, you can connect to a common residential 20 amp circuit. However, if you are running an air conditioning unit the 20 amp circuit will likey not be adequate.
Old 04-08-2010, 11:22 AM   #6
Actually that is incorrect. You can put a 30 amp receptacle on a 20 amp circuit. The breaker size is determined by the smallest rated component in the circuit.
The PVC will need to be 18" deep, if you use rigid metal or intermediate metal conduit you would only need to be down 6"
hayewe farm is offline   Reply With Quote
Old 04-08-2010, 12:01 PM   #7
You can't put a 20a receptacle on a 15a circuit
Nor can you put a 30a receptacle on a 20a circuit
See 210.21
You can put a 15a duplex receptacle (20a pass thru) on a 20a circuit
Old 04-08-2010, 12:56 PM   #8
See 210.21
Please provide the code it would violate. You can not use and underrated component on a circuit such as 15 ga wire in a 20 amp circuit but you can use and over rated component on a circuit such as 12 ga wire in a 15 amp circuit. The only exception is the use of a 15 amp receptacle on a 20 amp circuit. The breaker determines the capacity, even if you use a 30 amp receptacle you would not be able to draw more than the 20 amps.
Old 04-08-2010, 01:01 PM   #9
I did provide the code...not allowed
Old 04-08-2010, 01:05 PM   #10
Cute, but not an answer. 210.21(B) 1
Old 04-08-2010, 03:21 PM   #11
For those that don't have a copy of the NEC
210.21 (B) (1) Single Receptacle on an individual Branch Circuit.
A single receptacle installed on an individual branch circuit shall have
an amperage rating not less than that of the branch circuit.
It doesn't say not more than the branch circuit.
Wiring diagram for three-way switches with pilot light SaxTeacher Electrical 34 09-15-2013 08:53 AM
Cloth Wiring - Replace? JessicaGus Electrical 9 09-23-2009 07:45 PM
electric wiring in house remodel wis_remod Electrical 6 04-02-2009 03:40 PM
New Home Wiring - Seeking Expert Advice Dirtrnr Electrical 3 02-10-2009 11:33 AM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 08:52 PM