My questions is we are taking out our old gas cooktop and replacing it with a full induction cooktop. The specs are 3 wire 240/208 volt 60 hertz. I am wondering what gauge wire to se and also what size breaker to use? The place that sold it to me said I would need a 60 amp breaker? That seems pretty big for these requirments does it not? Thanks for your time and have a great day.
yamaman is offline   Reply With Quote
Old 10-29-2010, 10:06 AM   #2
Licensed Pro
Need more info
You need the KW rating of the cooktop to determine the circuit size.
Old 10-29-2010, 10:19 AM   #3
Alright I looked on the bottom of the cooktop and it says the following
120/208 6.70KW
120/240 7.70KW
SO I would probably go off of the 7.70KW to be safe right?
Old 10-29-2010, 10:24 AM   #4
and i see now that there is 10awg wire off the cooktop so that would probably be sufficient to run from the panel I assume?
Old 10-29-2010, 11:25 AM   #5
Rewards Points: 330
that unit draws 32 amps.#10 wire is good for 30 so you need #8 wire.
oleguy74 is offline   Reply With Quote
Old 10-29-2010, 11:42 AM   #6
You will need 8/3 with ground. 2 hots, a neutral and a separate ground. Code no longer allows using neutral as ground. Check installatin instructions. Some cooktops still come from factory with neurtal bonded to ground. If yours is that way you will have to change it. You will need a 40 amp double breaker.
SleepyDog is offline   Reply With Quote
Old 10-29-2010, 11:49 AM   #7
Thanks guys ok my stove only has a 3 wire coming off it red black green the two hots and ground but you are saying I need a 4 wire basically am I going to be able to hook that up to my stove wiring?
Old 10-29-2010, 12:44 PM   #8
I=E/R
a7ecorsair's Avatar
Is this a new cook top? Why does it have wires attached to it already?
a7ecorsair is offline   Reply With Quote
Old 10-29-2010, 12:58 PM   #9
Rewards Points: 330
no big deal.these are set up for hard wire.
Old 10-29-2010, 01:01 PM   #10
A "Handy Husband"
rjniles's Avatar
This is a 240 volt device and does not require a neutral (if you are stating the specs correctly). It is wired with a manufacturer installed whip that is intended to connect to the wiring from the panel in a junction box - no receptacle or cord like a free standing range would use.
7.7 KW is a bout 32 amps at 240 volt AC. The 208 volt rating is for 3 phase service which is pretty rare in a residence. The wires installed by the manufacturer in the whip is not an indicator of the the wiring you need from the panel.
The minimum requirements you need are 8-2 cable with ground (or equivalent if you need conduit) from a 40 amp 2 pole breaker in the panel. 2 hots from the 2 pole breaker and the bare ground connected to the ground bar. You do not need a neutral (white wire).
That being the minimum; I would wire this with 6-3 + ground cable. That would allow a change-out to a different cooking appliance of larger capacity that does need a neutral.
And our thanks to selena1 for you inane post about the Koran
My electrical answers are based on 2014 NEC, you may have local amendments.
The Following User Says Thank You to rjniles For This Useful Post:
yamaman (10-29-2010)
Old 10-29-2010, 02:15 PM   #11
rjniles thanks so much. What I am probably going to do is bring a 6-3 all copper cable from the 40amp 2 pole breaker bring it up to a junction just under the stove and the connect the "Whip" as you call it into the junction. I will bring the electrition out to double check everything after I have it all done I can just save alot of cost by running this myself. Thanks alot everyone, I am really liking this site so far.
Old 10-29-2010, 02:22 PM   #12
A "Handy Husband"
rjniles's Avatar
The only thing I would add is to cap the white wire with a wire nut- definitely at the cook-top end and in the panel to indicate a pure 240 volt circuit.
Old 10-29-2010, 04:12 PM   #13
Electrical Contractor
kbsparky's Avatar
There is a big difference between the cost of 6/3 and 8/2 wire, if you don't mind paying for capacity you don't need.
While #8/2 might be considered "code minimum" it's max. capacity is way beyond your appliance's rating -- at full power at that.
-KB
Old 10-29-2010, 04:55 PM   #14
Civil Engineer
Rewards Points: 5,246
I wired a similar cooktop. Only thing I would add is that the means of connection in the junction box for #6 wire to the whip typically uses a split connector, not a wire nut. At least that is what I used, the cooktop installation manual specifically required a split nut connection, and actually included directions on how to properly insulate the split nut connection using rubber tape plus wrapping tape.
Old 10-29-2010, 05:51 PM   #15
I=E/R
a7ecorsair's Avatar
The OP had two posting:
120/208 6.70KW
120/240 7.70KW
Doesn't this mean he needs the white wire?
Cooktop and Stand Alone Oven Wiring Replacing Existing Single Range/Stove Combination ffauth Electrical 3 08-23-2010 09:03 PM
Cooktop wiring upgrade Booron Electrical 7 12-08-2009 01:43 PM
Cooktop wiring debubba Electrical 3 11-20-2009 07:58 PM
Wiring Cooktop and Under Counter Oven Preach_2 Electrical 18 03-19-2009 04:30 PM
Wiring a 240v Delonghi cooktop cape45 Electrical 12 11-08-2007 02:38 PM