I am installing a sub panel in my house and running the wire through the attic. I am planning to run THNN wire in PVC conduit or SE cable. Since the circuit will be breaker protected I am thinking SE cable is OK. However if I use PVC conduit and pull the wires I can save some money and of course my labor is free.
Are both or either of these solutions code compliant? I live in Oklahoma and the attic probably gets around 140F
mccorb101 is offline   Reply With Quote
Old 10-09-2017, 04:51 PM   #2
Super Moderator
joed's Avatar
Rewards Points: 404
Re: Wires in conduit or SE cable
A sub panel needs a four wire feed. I think SE is only three wire so it would not be permitted for this use.
Old 10-09-2017, 04:57 PM   #3
A "Handy Husband"
rjniles's Avatar
Rewards Points: 984
You need SER cable which is 4 wire.
J. V., Jim Port and mccorb101 like this.
My electrical answers are based on 2017 NEC, you may have local amendments.
Old 10-09-2017, 05:22 PM   #4
Rewards Points: 18
Sorry. I meant SER. Also what about the PVC conduit?
Old 10-09-2017, 05:27 PM   #5
Super Moderator
joed's Avatar
Rewards Points: 404
PVC would be fine.
mccorb101 likes this.
Old 10-09-2017, 09:13 PM   #6
Disrespectful to dirt
Fishbulb28's Avatar
Rewards Points: 2,148
It's too hot for PVC conduit - it's limited to 122F. You would need to use EMT.
Oklahoma is on the 2014 NEC. In this version, SE cable run in insulation is restricted to using the 60C ampacity column. This means you would need to run much larger cable unless you can remain clear of the insulation in the attic.
Aluminum SER is usually the least expensive option even with the larger cable requirement.
Fishbulb28 is offline   Reply With Quote
Old 10-10-2017, 10:31 AM   #7
Rewards Points: 18
Ok. SER cable it is. So I guess I can hang it from the rafters using staples to keep it out of the insulation. Is this ok?
Old 10-12-2017, 03:38 PM   #8
Fishbulb28's Avatar
Yes. It needs a staple, SE bracket, or other support every 4 1/2 feet. Also make sure each length passing through the attic insulation is less than 10 feet.
Tags
conduit , service entrance cable , subpanel , thnn
Wires all mixed up Bucksco3433 Electrical 21 03-08-2017 08:18 PM
Securing Cable and Conduit Problem bergs4 Electrical 4 08-07-2011 02:50 PM
MC cable through conduit StudebakerHawk Electrical 3 03-05-2010 10:38 AM
SubPanel-NM Cable in Conduit? blankcek Electrical 9 06-24-2008 10:41 AM