For a feeder that short, replacing it with 1/0 AL to make it 100A would not cost too much. I installed a 60' length of #1 SER only to read that is it rated for 85A under NEC 2008. Rather than replacing the cable, I just installed the next size larger standard breaker (90A).
H2O Engr is offline   Reply With Quote
Old 03-09-2010, 12:31 PM   #32
Master Electrician
Rewards Points: 5,084
That's acceptable if your calculated load is less than or equal to 85 amps, the ampacity of the cable.
brric is offline   Reply With Quote
Old 03-09-2010, 12:40 PM   #33
Rewards Points: 214
I need to look on my receipt. The thing is when I bought the cable I told the guy that I wanted #2 copper for a 100amp sub panel that I was wiring. He said they only had aluminum. I said ok, I'll take aluminum and he looked at his chart and gave me the wire. I thought he told me it was rated for over 100amp. But then again I thought he called it #1. I am going there today to pick up the adapters to redo my neutral and ground and nipple. The thing is I untwisted the ground into 3 separate pieces to fit in the terminals and I won't be able to get them twisted tight again. I will have to buy another wire for my ground. What type wire and size should I get for my ground?
Thanks.
Abs777 is offline   Reply With Quote
Old 03-09-2010, 12:57 PM   #34
Master Electrician
Thanks.
#8 Cu stranded or solid bare
Old 03-09-2010, 05:03 PM   #35
Rewards Points: 214
I checked out my receipt and it is SER 1/0-1/0-1/0-2 wire. I talked to the guy when I went and bought the lug adapters and he said it was rated from 100-135amps. So I think I am good there and don't need to change my wires. I am going to try to correct the neutral and ground with the adapters and that should take care of everything. I don't need a nipple or conduit between the two panels, do I?
Old 03-09-2010, 05:09 PM   #36
Yup 1/0 is Ok
Old 03-09-2010, 06:17 PM   #37
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
Originally Posted by busman View Post
What's holding the subpanel to the wall?? A single nail?? Construction adhesive?
Mark
yeah,i missed that!
plummen is offline   Reply With Quote
Sub Panel install eagertolearn Electrical 17 01-23-2010 05:39 PM
100 -> 200 amp panel upgrade questions philipjcaputo Electrical 1 10-30-2009 03:35 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
Panel Placement In Outbuilding smitty286 Electrical 3 03-31-2008 12:20 PM
breaker panel question chadvavra Electrical 11 08-10-2007 09:20 AM