Wired Up My Sub Panel (pics) - Electrical - DIY Chatroom Home Improvement Forum
Old 03-09-2010, 06:45 AM   #1
Rewards Points: 214
Wired up my sub panel (pics)
Just wanted to make sure everything looks ok. Let me know if you see any red flags. Thanks Scuba_Dave and everyone else who gave me info. Saved me quite a bit of cash.
Abs777 is offline   Reply With Quote
Old 03-09-2010, 06:49 AM   #2
Master Electrician
Rewards Points: 5,082
Looks very nice. What size breaker and wire did you use?
brric is online now   Reply With Quote
Old 03-09-2010, 06:50 AM   #3
Rewards Points: 29
Why is your ground landed on the neutral bar?
jsmith929 is offline   Reply With Quote
Old 03-09-2010, 06:50 AM   #4
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
looks nicer than the main panel so far! id suggest running a piece of conduit to connect the 2 panels since theyre surface mounted
plummen is offline   Reply With Quote
Old 03-09-2010, 06:52 AM   #5
plummen's Avatar
ground is mounted on its own buss on left side of panel
Old 03-09-2010, 06:52 AM   #6
Looks good
Not sure which panel you mean
But in the main panel grounds & neutrals can be mixed
In the sub they are seperate & he has wired them that way
Old 03-09-2010, 07:10 AM   #7
Rewards Points: 214
Thank you. I used 100amp breaker and #1 four conductor aluminum wire. I wanted copper, but the electrical supply store I bought everything from only carried aluminum that size.
Old 03-09-2010, 07:16 AM   #8
Master Electrician
Most of the current consensus is that #1 Al is only rated for 85 amps in your application but i'm sure it won't be a problem unless your inspector catches it.
SER must be sized according to the 60 deg column in 310.16
Old 03-09-2010, 07:33 AM   #9
Rewards Points: 774
Two neutrals in one terminal (main panel) is a violation (and a good way to destroy most of the electrical appliances in your home). Also splitting strands on the ground wire to get it into two terminals is a violation.
Mark
busman is offline   Reply With Quote
Old 03-09-2010, 07:38 AM   #10
Rewards Points: 774
What's holding the subpanel to the wall?? A single nail?? Construction adhesive?
Mark
Old 03-09-2010, 07:53 AM   #11
Rewards Points: 214
I did not know that. My electrician told me to get #2 copper or #1 aluminum. I asked the guy at the electrical supply place if that was right and he said it was. So then should I go buy copper and redo it?
The wire is so thick it won't fit into a single terminal, what is the proper way to do this?
In the picture it was a middle screw while I wired it and leveled it. Now it is 4 screws.
Old 03-09-2010, 08:01 AM   #12
Rewards Points: 774
There are various sorts of adapter terminals (different for each manufacturer) that can provide a larger terminal on neutral/ground bars.
This is the only legal correction.
For the wire size, your electrician was probably assuming you would use a nipple to attach the panels and individual wires. You would not have the 60 degree limitation in this case. By using SE cable, you are limited to 60 degrees.
Mark
Old 03-09-2010, 08:02 AM   #13
NEC table, cable uses the 60 degree column which is only 85a
Old 03-09-2010, 08:07 AM   #14
Rewards Points: 774
Not ALL cables. Just NM and SE cables - and AC cable in insulation.
Mark
Old 03-09-2010, 08:09 AM   #15
Master Electrician
Purchase a couple of Siemens part # ECLK2 terminals and install them on the neutral bar to accomodate the larger wires.
Sub Panel install eagertolearn Electrical 17 01-23-2010 05:39 PM
100 -> 200 amp panel upgrade questions philipjcaputo Electrical 1 10-30-2009 03:35 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
Panel Placement In Outbuilding smitty286 Electrical 3 03-31-2008 12:20 PM
breaker panel question chadvavra Electrical 11 08-10-2007 09:20 AM