I don't think you understand what I'm suggesting by using a 15 amp MWBC but the OP has already ran the #12 from the panel ... so Jims suggestion is likely his best bet.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 07-17-2010, 11:18 PM   #17
Electrician
Proby's Avatar
Originally Posted by Stubbie View Post
Proby
I understand what you are saying, but if we are trying to be code compliant here, 2 15A circuits will not fill in for a required 20A circuit.
Proby is offline   Reply With Quote
Old 07-18-2010, 12:39 AM   #18
UAW SKILLED TRADES
Stubbie's Avatar
The issue is are we thinking outside the box and violating the NEC as to following manufacturers instructions which are calling for a 20 amp dedicated circuit to the unit. The other problem is we have fixed space heating which requires a continuous load calculation for the heater. All this considered requires #12 conductors ... and protection according to 240.4D.
So I concur it would not be code compliant to use a 15 amp Multiwire branch circuit.