Originally Posted by Proby View Post
Stubbie, are you sure about those ampacities?
Yes .. but I think you feel there is an error. So I am open to what that error is if you would point it out.
I base the ampacities I listed on the provisions provided by 110.14 (C). This is assuming that I have 75C terminations at both panels. Technically not knowing that information would require 60C ampacities. So in that respect I'm on shakey ground....
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 08-13-2010, 05:40 PM   #17
Electrician
Proby's Avatar
Sorry Stubbie, I just noticed your reply today.
EDITED, incorrect information.
Anything fun is either illegal, immoral, or fattening.
Proby is offline   Reply With Quote
Old 08-13-2010, 07:08 PM   #18
UAW SKILLED TRADES
Stubbie's Avatar
I don't agree at all ...
How do you intrepret 240.4(B) and the 3 requirements. If I have a 55 amp conductor in table 310.16 I am allowed for a feeder using #6 UF-B to use a 60 amp breaker because its ampacity (55 amps) does not fall on a standard fuse size in accordance with 240.6(A)...no?
Stubbie
Old 08-14-2010, 08:07 AM   #19
Electrical Contractor
jbfan's Avatar
Rewards Points: 980
I agree, and never failed an inspection using this method!
Yes I am a pirate, two hundred years too late
The cannons don't thunder, there's nothing to plunder
I'm an over-forty victim of fate.
Old 08-14-2010, 09:28 AM   #20
Electrician
Proby's Avatar
I've been looking into why I thought that way. From what I can tell, you can't upsize the breaker if the calculated load is higher than the cable's ampacity. In all other cases you can. You were right Stubbie. I really don't know why such an elementary code issue has me confused.
Old 08-14-2010, 02:01 PM   #21
UAW SKILLED TRADES
Stubbie's Avatar
Hey it happens.... No sweat. Speaking of feeders they only have to be capable of carrying the calculated load. If the calculated load is more than the ampacity of the feeder then your going to have to upsize the feeder. I never try to 'squeeze' a feeder to meet a calculated load... give yourself some room.. In many cases a 60 or 70 amp feeder is fine to a 4 space 70 amp panel that uses tandems for 120 volt circuits.. #6 thhn/thwn on 60 or 70 amp breaker. Depends on how many expected 240 volt circuits the customer needs. But many garages doubling as small hobby shops fall in this catagory.
Anyway getting back on the subject a little.... I have two file links I saved that kinda goes over all this.... I go back to it quite often when I get a little fuzzy on what we have been discussing.. I'll post them and you can save for yourself.
One goes into a lot of other considerations and one is less detailed. You will notice in the detailed article that it isn't always as simple as "next size' up' ... and remember to that feeders supplying only motors are 'next size down' .. So no surprise at all when I hear it is confusing .. I've been there myself many times.
I'm posting these because they are excellent references not because I think you need them. Given time on this forum your going to catch me (if you haven't already) in one of those fuzzy moments ...and return the favor....
Sizing Conductors for All Load Conditions | IAEI Magazine Online
Overcurrent Protection for Conductors | IAEI Magazine Online
And here are a couple good ones for motors and the calculations required
Motor Calculations Part 1: Motors and Branch-Circuit Conductors
Motor Calculations Part 2: Feeders
Stubbie
The Following User Says Thank You to Stubbie For This Useful Post:
Proby (08-14-2010)
cooling detached shop cbzdel HVAC 1 05-17-2010 06:02 PM
Real Basic Electrical question re: neutral wire hellothere123 Electrical 22 07-21-2009 06:07 PM
New Stove, old wires - 2 wire vs 3 wire DIYGST Electrical 22 03-02-2009 04:13 PM
Dryer Grounding??? Traci_howdyadothat Electrical 7 05-27-2008 01:14 PM
Installing Fluorescents in Garage rzrbkpk Electrical 26 04-08-2008 09:00 PM