Voltage Across Hot And Neutral With Brkr Open - Electrical - DIY Chatroom Home Improvement Forum
Old 10-10-2009, 01:03 PM   #1
Voltage Across Hot and Neutral with Brkr Open
I have a panel with bonded neutral and ground. A 14-3 without ground is connected to two 15 amp single pole breakers. They leave the panel and split in a junction box. The circuit on the black leg reads 120v. When you open that breaker the circuit reads 40v. When you open both breakers the circuit reads zero.
Any suggestions on the root of the problem and where I begin to trace it down. Some of the runs disappear into the wall so their destination cannot be easily determined.
Pulipeople is offline   Reply With Quote
Old 10-10-2009, 01:39 PM   #2
Are you using a digital meter? You may be reading phantom voltage from the other circuit.
jerryh3 is offline   Reply With Quote
Old 10-10-2009, 01:43 PM   #3
Yes, I have a Fluke digital meter. I can pull out my old analog and try it. Should analog be accurate?
Old 10-10-2009, 02:08 PM   #4
Rewards Points: 2,998
Do you know any receptacles connected to that circuit? Plug in an incandescent light and switch it to on. Now when the breaker is switched off you should not measure any phantom or induced voltage.
Stop some of your bank autopayments so you can set priorities for manual monthly payments out of your coronavirus stimulus check.
Old 10-10-2009, 03:47 PM   #5
Yes. Try the analog and see what you get.
Old 10-11-2009, 10:20 AM   #6
Either meter should be loaded down with an incand. bulb.
Old 10-14-2009, 08:16 AM   #7
Thanks to everyone who replied to my post. The problem is resolved! I placed an incandescent bulb on the circuit and read the voltage with my digital meter. The voltage was nil. Steve